Interrupt Job
  • Jrk
  • January 30, 2024 at 8:08 AM
  • Jrk
    21
    I have a question about interrupt job on NX100 controller.
    Instead of looking input signal to be TRUE,
    I want to trigger interrupt job when input signal switches to FALSE.
    What is the simplest way to achieve that?
  • Go to Best Answer
  • ljuba
    33
    5
    281
    • January 30, 2024 at 1:15 PM
    switch it in ladder
  • Jrk
    21
    • January 30, 2024 at 2:31 PM
    Thank you for your reply!
    I check concurrent IO documentation, and want to check if I understood correctly + some additional questions
    Actual set of commands regarding input that I want to use:
    GSTR #20030
    GOUT #00030
    From my understanding an input Relay group of 8 #20030 is now connected to group #00030 (and in this group is signal that I want to see negated)
    From this group I want only one signal on Relay 20037 to connect negated to "some variable" with command so I plan to add lines:
    STR-NOT #20037
    OUT #"variable"
    Here I have 2 questions:
    1. Since this is ladder like in PLC, there is no problem with "reading" same variable 2 times (so it won't influence first set of commands: GSTR #20030 OUT #00030) ?
    2. What variable can I use, where to declare BOOL variable for my OUT, or can I just use some Auxiliary Relay signals that are not already used?
    And in the end in the interrupt for Input signal I will put this "new variable"
  • 95devils
    235
    8
    1,951
    • January 31, 2024 at 12:29 AM
    Are you sure you ladder is mapped as
    GSTR #20030
    GOUT #00030
    and not
    GSTR #20030
    GOUT #00010?
    Assuming standard mapping step 1 is to delete the:
    GSTR #20030
    GOUT #00010
    Step 2 is to write the following:
    STR #20030
    OUT #00010
    STR #20031
    OUT #00011
    STR #20032
    OUT #00012
    STR #20033
    OUT #00013
    STR #20034
    OUT #00014
    STR #20035
    OUT #00015
    STR #20036
    OUT #00016
    STR #20037
    OUT #00017
    Step 3 is to compile. Your ladder is back to the way it was but with group 1 broken out.
    Write your logic for whichever Universal Input you wish to use as the trigger for the interrupt job.
  • 95devils
    235
    8
    1,951
    • January 31, 2024 at 12:34 AM
    Quote from Jrk
    1. You can read the same address as many times as you want. You can only write to the address once.
    2. The only addresses you can use with interrupt job is an Universal/General Purpose Input.
    Interrupt Job was developed for press tending. The input is the press starting to roll which is a rising edge signal.
  • Jrk
    21
    • January 31, 2024 at 7:28 AM
    Thank you, now everything is clear, can't wait Saturday to test it.
    Quote from 95devils
    GSTR #20030
    GOUT #00030
    and not
    GSTR #20030
    GOUT #00010?
    You are correct, actual map is with GOUT#00010.
    Quote from 95devils
    Yes, this makes sense.
    I want to use interrupt to stop the program when air pressure is lost and my pressure sensor has only one NO switch.
    I could connect it to a new hardware relay and use NC contact as input, but I figure it must be possible to do it with software.
  • 95devils
    235
    8
    1,951
    • January 31, 2024 at 12:46 PM
    • Best Answer
    Quote from Jrk
    That’s 10x the work for this. Depending on the application the controller is set up for there may be a dedicated set of terminals for air pressure.
    If not a simple user alarm would suffice. One or two rungs added to the ladder. Add the text to display on the screen.
    Advantages to this are:
    No breaking out input groups.
    No adding EI and DI instructions in a job.
    No creating the job that will execute on the interrupt.
    No additional Jump/Call job.
    No Clear instruction.
    No assigning the interrupt input.
    No assigning the executing job on the interrupt.
  • Robodoc
    56
    7
    1,062
    • February 3, 2024 at 2:36 PM
    run your input through a relay
    Robodoc
  • Jrk
    21
    • February 12, 2024 at 11:04 AM
    Quote from 95devils
    Finally found time to tinker with ladder editor over last weekend, and it went smoother than I taught.
    Thank you for pointing out the user alarm option, it work's like a charm.
Similar Threads
  • Interrupt Job Not Working
    • Jack82
    • September 13, 2023 at 9:34 PM
    • Yaskawa Motoman Robot Forum
  • Test an Interrupt Job in Motosim
    • StachLee
    • June 27, 2023 at 12:06 PM
  • Interrupt or other mechanism to reset program
    • krzych
    • February 15, 2014 at 9:26 AM
  • Macro job (suspend job)
    • Denis-motoman
    • January 30, 2023 at 10:39 AM
  • Cancel Program and Send Pointer to Cell.
    • PGG
    • August 31, 2017 at 10:40 PM
    • KUKA Robot Forum
  • Hold from external input
    • dset
    • January 20, 2022 at 6:21 AM
  • Unintended motion
    • Robottech
    • February 2, 2021 at 12:28 AM
  • INTERRUPT ON BETWEEN PTP C_PTP
    • rvsh
    • May 30, 2020 at 3:31 PM
    • KUKA Robot Forum