I keep getting this error on power up of the robot and plc. am i missing a setting or something for this if i do a driver reset it all works fine . only on power up and on both robots
KRC4 El6695 error on power up
-
the leg -
June 25, 2021 at 1:52 PM -
Thread is Unresolved
-
-
Never seen that exact one before. Is this a KRC4 Compact? Most of the times I ran into an EL6695 error was b/c the Compact comes with no power wired for the Beckhoff module that provides the Digital I/O option.
-
how is it powered?
-
The power is from the the plc cabinet as the EK1100 is mounted in the control cabinet.
When I power the plc cabinet up it also powers up the robots .
-
This is standard size KRC4
-
-
try powering bus coupler from KRC
-
Does the EK1100 power up at all?
-
Does the EK1100 power up at all?
Yes it all works with no issues only sometimes on power up i get the error . do an i/o reconfig and boom all working again. doesn't happen all the time maybe 50% of time it fails on power up
-
try powering bus coupler from KRC
try powering bus coupler from KRC
That was going to be my next thing to try on my return