Program selection pns on RJ3iB
  • camillep
  • March 23, 2022 at 12:52 PM
  • camillep
    18
    Hi everyone,
    There you go when I launch my robot in automatic mode, he puts himself defaults, the MEMO-073 program does not exist. He is looking for PNS0008 but my program is PNS0001. I don't know how to do for him search the PNS0001. I have a fanuc 100ib with RJ3iB controller. Please help me. I hope my English is not so bad and you can undestand me.
    Edited 3 times, last by camillep (March 23, 2022 at 1:05 PM).
  • DS186
    199
    1,051
    • March 23, 2022 at 1:32 PM
    Check your PNS1-8 inputs for the correct signal state. To select PNS0001 only input PNS1 must be TRUE and PNS2-8 must be FALSE.
  • camillep
    18
    • March 23, 2022 at 2:02 PM
    ok thanks, so my UI 9 to 11 PNS1 to 3 are OFF my UI 12 PNS 4 is ON and UI 13 to 16 PNS 5 to 8 are *, I don't know how tu put them at ON.
  • DS186
    199
    1,051
    • March 23, 2022 at 2:07 PM
    That explains why the controller is looking for PNS0008. How are the PNS inputs connected? Hardwired, controlled by a PLC? If so, which protocol is used, Ethernet/IP, PROFINET, etc.?
  • camillep
    18
    • March 23, 2022 at 2:11 PM
    controle by a PLC, and i don't know which protocol is used
  • DS186
    199
    1,051
    • March 23, 2022 at 2:30 PM
    In that case I guess the PNS signals are also controlled by the PLC. You or the PLC programmer should check that signals on the PLC side.
  • camillep
    18
    • March 23, 2022 at 2:54 PM
    i come checked and i think is hardwired, in my PLC i control just PNS1 and not other
  • HawkME
    568
    10
    3,268
    • March 23, 2022 at 7:00 PM
    If it is hardwired then it is either wired to the wrong input, or your UI config on the robot is setup incorrectly.
  • pdl
    266
    1,506
    • March 23, 2022 at 11:16 PM
    As an easy workaround, you could just copy pns0001 to pns008. This isn't a real fix, but it will get your robot running.
  • camillep
    18
    • March 24, 2022 at 12:16 PM
    Quote from pdl
    Yes i did that, but my company prefers to be in PNS001
  • camillep
    18
    • March 24, 2022 at 12:20 PM
    • #11
    Quote from HawkME
    i think it's second solution but i don't know how correct my config
  • DS186
    199
    1,051
    • March 24, 2022 at 1:39 PM
    • #12
    Quote from camillep
    Can you post a screenshot of the UI config. With that it ist easier to guide you. Select MENU > I/O > UOP, display the UIs and then click CONFIG to show rack and slot.
  • camillep
    18
    • March 24, 2022 at 2:35 PM
    • #13
    Here the screenshot of the UI config.
    Images
      • 195.6 kB
      • 900 × 1,200
      • 19
  • HawkME
    568
    10
    3,268
    • March 24, 2022 at 6:29 PM
    • #14
    That image shows UOP Out, we need to see UOP In.
  • hermann
    405
    2,596
    • March 24, 2022 at 8:17 PM
    • #15
    And one can nearly nothing detect. Make a better picture.
  • camillep
    18
    • March 25, 2022 at 12:39 PM
    • #16
    Quote from HawkME
    Cette image montre UOP Out, nous devons voir UOP In.
    Désolé j’étais trop rapide, je n’ai pas fait attention
    Images
      • 322.65 kB
      • 1,920 × 1,145
      • 9
  • camillep
    18
    • March 25, 2022 at 12:40 PM
    • #17
    and the second
    Images
      • 313.01 kB
      • 1,877 × 1,200
      • 12
  • HawkME
    568
    10
    3,268
    • March 25, 2022 at 3:03 PM
    • #18
    So your Robot is setup to get 4 signals from the PLC for PNS 1-4. The PLC is turning on number 4 instead of 1. There are 3 solutions.
    1. Have the PLC turn on 1 instead of 4.
    2. Swap the physical wiring of 1 and 4
    3. Change the Robot UOP so that UI 9 is assigned to start 16, and UI 10-12 are unassigned.
    It sounds to me like you will probably do #3 above. But it also sounds like you don't understand why the system is setup the way it is. Whoever designed this obviously had a plan for which signals the PLC would send and how it would be wired. The correct solution would be to understand those first, then correct the issue.
  • camillep
    18
    • March 25, 2022 at 3:58 PM
    • #19
    thanks, no i don't undestand why the system is setup in this way. when i arrived on this project the program was PNS0001. I have a default SERVO-037 SERVO IMSTP input, that i have settled in change UOP auto assignment in full (CRM79) to simple (CRM79), that i had change in other direction the day before
  • Rj3ib
  • pns