Hello guys, we are having trouble with a Irc5 welder with IRBP type D positioner.Turnin the key to auto it shoes an mesage refering to a simulate signal and did not go when we reset the Operator ready button, can anyone tell us how to find the sumulated signal and reset it?
IRC5 simulated IO
-
Enio -
December 28, 2021 at 7:50 AM -
Thread is Unresolved
-
- Go to Best Answer
-
Click on the menu button on the FlexPendant and select inputs and outputs. There you can click on view and then select simulated signals.
-
DS186's answer is entirely correct. Moreover, there is a system parameter setting that you can change to avoid this event in the future. Open the control panel, navigate your way to controller, Auto Condition Reset. Select AllDebugSettings, make it TRUE. When switching to Auto, it will unsimulate all IO, return the PP to Main if the calling heirarchy is not based on Main (someone set PP to routine other than main) and set the speed override to 100% if it has been reduced.
-
Lemster68
December 28, 2021 at 2:03 PM Changed the title of the thread from “IRC5” to “IRC5 simulated IO”. -
Thanks Guys,the problem was solved easyly thanks again
-
Hello guys, it turns out that this simulated signal needs to be in order to activate the CMT power source, is there any way to keep it simulated even on auto mode? I actually set it with a set instruction on the head of each routine but it does seams right thing
Thanks
-
Is it a simulated INPUT or OUTPUT?
-
it is digital output
-
What about switching the output with a cross connection or an event routine?
-
There should not really ever be a need to simulate an output as you can turn them off and on as needed. The effect of simulating an output is that the signal does not ever turn on. It may show 1, but the voltage is not applied to the output signal.
-
What type of digital IO, discrete (voltage) or networked?
Ethernet/IP outputs have been simulated here and have been accepted by the connected PLC. However, this example is not a welding system.
-
- Best Answer
Robot studio I/O System ,or from TouchPanel, change Acces Level from Default to ALL,
you ca Force the output in AutoMode