Yesterday I deployed a project, changing from EthernetIP to ProfiNET.
WV didn't have any issues/Errors. Controller looked like it rebooted to initialize drivers and such.
KSS splash screen came up, then it took a KRCDiag, and popped the error message.
"Unhandled Error
The following error occurred while communicating with the kernel system:
$CONFIG not correct ($CONFIG |/R1/System/Collmonlib.dat/LEARN_MODE)
The application must be shut down."
KSS 8.6.6
HMI 8.6 B0296
Kernel KS V8.6.296
I have included images of the error, I typed it out so it's searchable in the future.
I am unable to deploy a new project. I removed the projects in C:\KRC\USER\ProjectRoot\ and ran C:\KRC\UTIL\InitalProjectSetup\InitalProjectSetup.exe as admin. This succeeded from what I can tell, but the error remains.
I've looked for the Collmonlib.dat, I've looked for LEARN_MODE...
I'm out of ideas, and I know the answer is going to be to use the USB... which I don't have.
Thanks in advance SkyeFire & panic mode!
Cheers!