    Hello there,
    Let me introduce myself, I am a student in the Factory Automaton program and new to robotics.
    I am working on a project with the following equipment from FANUC:
    1. FANUC Robot LR Mate 200iD/4S Educational Cell
    2. R30iA Mate Controller - Software version between 8.0 and 9.0 not sure
    3. PC Windows 10 - Python app
    The following picture tries to explain the use case of the project on which I am currently working
    the aim is to control robot movement and picking tasks from the cloud and generating alerts if the robot is unable to approach a specified position. There are two apps in the work scene App1 and App2. App2 will be controlling the robot by processing the data obtained by App1.
    As the robot operation is based on vision so App1 needs to pull some data from the robot related to image, vision registers, U/T frames, and position register which will be utilized by App2 for computing possible forward/inverse kinematics solutions, analyzes and reports the reachability of positions, and validate trajectories given by the AI algorithm running in App2 and based on selected trajectory movement instructions will be created and send to the App1 which command the robot to move to verified picking position.
    Currently, my focus is to establish communication between robot and the Python app (App1) running on PC to get the following data from robot and sending movement instructions.
    1. Snap image data (Not sure, this data is possible to extract or not)
    2. Positions of the detected object (as far as I understand from the manual, this information is available in the vision register)
    3. status of system variables (specifically related to robot reachability), for example, if an object is placed at the corner of the solitaire board, where the robot cannot reach, and the robot does not move, and the user is warned by the alarm on teaching pendant
    4. VR and PR data
    5. UF and UT frames
    Also, the FANUC manual and some posts from this site got a glimpse that this could be done using socket messaging. Based on my task I make the robot a socket server and App1 as a socket client and wrote a simple KAREL server code and was able to exchange strings between the robot(roboguide) and App1.
    KAREL server code
    PROGRAM send2Cliient
    %STACKSIZE = 4000
    %COMMENT =  'AheadUtilityr'
    %NOLOCKGROUP
    %NOPAUSE=ERROR+COMMAND+TPENABLE
    %ENVIRONMENT uif
    %ENVIRONMENT sysdef
    %ENVIRONMENT memo
    %ENVIRONMENT kclop
    %ENVIRONMENT bynam
    %ENVIRONMENT fdev
    %ENVIRONMENT flbt
    %INCLUDE klevccdf
    %INCLUDE klevkeys
    %INCLUDE klevkmsk
    --DECLARACION DE VARIABLES
        VAR
            ARCHIVO2 : FILE
            TMP_INT : INTEGER
            TMP_INT1 : INTEGER
            TMP_STR : STRING[128]
            TMP_STR1 : STRING[128]
            STATUS : INTEGER
            ENTRY : INTEGER
            loop1 : BOOLEAN
    BEGIN
        -- clear the TPERROR screen
        WRITE TPERROR(CHR(128))
        --WRITE(CR)
        WRITE('DISCONNECTING..',CR)
        MSG_DISCO('S3:',STATUS)
        WRITE('DONE.',CR)
        SET_FILE_ATR(ARCHIVO2, ATR_IA)
        --SET THE SERVER PORT BEFORE DOING A CONNECT
        SET_VAR(ENTRY, '*SYSTEM*', '$HOSTS_CFG[3].$SERVER_PORT', 1162, STATUS)
        WRITE('CONNECTING..',CR)
        --OPEN CONNECTION
        MSG_CONNECT('S3:', STATUS)
        WRITE(' CONNECT STATUS= ',STATUS,CR)
        loop1 = TRUE
        --connectted or not
            IF STATUS = 0 THEN
                WHILE loop1 = TRUE DO
                         WRITE('Opening File...',CR)
                        OPEN FILE ARCHIVO2 ('RW','S3:')
                        STATUS = IO_STATUS(ARCHIVO2)
                        WRITE('File_IO_Status=',STATUS,CR)
                        --FILE OPEN is success OR NOT
                        IF STATUS = 0 THEN
                            --send msg to client
                            TMP_STR = 'RunJob'
                            WRITE ARCHIVO2(TMP_STR)
                            WRITE('Wrote: ',TMP_STR,CR)
                            WRITE('Waiting to read from client...',CR)
                                WRITE('READING',CR)
                                --reading from client
                                BYTES_AHEAD( ARCHIVO2, ENTRY,STATUS)
                                READ ARCHIVO2 (TMP_STR::ENTRY)
                    status = IO_STATUS(ARCHIVO2)
                    WRITE('Read status: ',status,CR)
                    WRITE('Read: ',TMP_STR,CR)
                    loop1 = FALSE
                    WRITE('Closed file.',CR)
                    CLOSE FILE ARCHIVO2
                        ELSE
                    WRITE('Error opening file',CR)
                    loop1 = FALSE
                        ENDIF
                ENDWHILE
          ENDIF
    --IF UNINIT(TMP_STR) THEN
        --WRITE ('UNINT',CR)
        --WRITE ARCHIVO2('result was UNINIT', CR)
        --WRITE('CLOSING File...',CR)
        --CLOSE FILE ARCHIVO2
        --STATUS = IO_STATUS(ARCHIVO2)
           --WRITE('File_Close_Status=',STATUS,CR)
    --ELSE
    --READ 10 BYTES
    --READ ARCHIVO2 (TMP_STR::10)
    --WRITE (STATUS,CR)
    --WRITE 10 BYTES
    --WRITE (TMP_STR::12,CR)
    --STATUS= IO_STATUS(ARCHIVO2)
    --WRITE (STATUS,CR)
    --                       ENDIF
    --                CLOSE FILE ARCHIVO2
    --                ENDIF
    --            ENDFOR
    --ENDIF
    END send2Cliient
    Python Client
    import socket
    HOST = '192.168.100.2'  # The server's hostname or IP address
    PORT = 1162       # The port used by the server
    with socket.socket(socket.AF_INET, socket.SOCK_STREAM) as s:
        s.connect((HOST, PORT))
        s.sendall(b'Hello from Client!')
        data = s.recv(126)
    print('Received', repr(data))
    Does this socket server-client is fine or there is some other easy method available?
    How the above-mentioned date can be extracted from the robot using KAREL and send to APP1? sending of the string is easy through file read/write but the position and frame are tricky to send.
    Regarding the KAREL server code, currently, it sends a string to the client and closes the communication but I want the server can listen to the client continuously but I am not able to do that, how I can achieve this functionality?
  • Go to Best Answer
  • jmd2777
    34
    193
    • September 24, 2021 at 7:31 PM
    That is a big project. You will have to spend time with the Fanuc manuals.
    I will give my advice
    Quote from mahboobelahi93
    Its probably fine to use the socket connection. There are easier methods but they require purchasing additional software.
    Everything will need to be formatted as a string. This is sometimes done using JSON, CSV, or XML formatting or you can design your own format. So the process will be 1) Use KAREL commands to get the value and 2) format into a string to send to client
    Image data - not reasonable to send through socket connection. There is a KAREL command "V_SAVE_IMREG" which will save a snapped image to file. Then you could use FTP to get the image.
    Positions of objects in VR - VREG_FND_POS command
    System variables - GET_VAR command
    Search the KAREL manual for similar commands to get the other data that you need.
    In your code, isn't "loop1 = FALSE" executed inside the WHILE loop unconditionally? That will cause the loop to exit. To keep the KAREL program running you need to continue looping.
    WHILE (loop_condition)
    BYTES_AHEAD(...)
    IF (bytes_available > 0)
    #read data
    #process data and take action
    ENDIF
    DELAY 10
    ENDWHILE
    SkyeFire
    1,052
    9,429
    • September 25, 2021 at 6:36 PM
    There might be an easier way than socket communications.
    KAREL supports remote program calling via URLs, like so: HTTP://robbot_ip_address/KAREL/Karel_Program_Name?VariableName=string
    '?' marks off a variable to be sent to the robot, which must be declared as a string variable in the KAREL program. 'string' is the string that that KAREL variable will contain once this URL is called.
    The KAREL program can write a string and pass it back to the computer opening the URL. It's an .HTML file, but internally it's nothing but plain ASCII strings, no formatting codes.
    I was able to communicate with my Fanuc in this way, bidirectionally, using just this much Python code:
    Python
    from urllib.request import urlopen
    URL = 'http://192.168.1.250/KAREL/(karel program name)'
    Response = urlopen(URL)
    String = Response.read().decode('utf-8')
    print (String)
    That would cause a single run of the KAREL program. Variables could be added to the end of the URL call separated by '?', up to a maximum of 10, IIRC.
    Feedback from the KAREL program required:
    BEGIN
    --     debug only
        IF UNINIT(chOutFileName) THEN
            chOutFileName='TD:RESPONSE.HTM'
        ENDIF
        Open file in Overwrite mode
        OPEN FILE fFileHandle ('RW', chOutFileName)
         --debug only
         WRITE fFileHandle ('chAction,')
         WRITE fFileHandle (chAction)
         WRITE fFileHandle (CR)
         WRITE fFileHandle ('iSelection,')
         WRITE fFileHandle ('Selection)
      -- Close file for return to browser client
         CLOSE FILE fFileHandle
    The CRs are KAREL keyword for carriage returns, and all the variables are strings. The CLOSE FILE command would return the string written into chOutFileName to the browser or program that called the URL.
    The filename written to must be TD:RESPONSE.HTM, this is a "handle" to the robot's internal web server for the exchange opened by the URL.
  • mahboobelahi93
    82
    • September 27, 2021 at 1:52 PM
    Quote from jmd2777
    BYTES_AHEAD(...)
    #read data
    ENDIF
    DELAY 10
    ENDWHILE
    Thanks, JM for your response.
    I tried your suggestion, now the server is continuously running but client does not connect again and I received the following error on Python side:
    ConnectionRefusedError: [WinError 10061] No connection could be made because the target machine actively refused it
    BEGIN
        --WRITE(CR)
        WRITE('DONE .',STATUS,CR)
        SET_FILE_ATR(ARCHIVO2, ATR_READAHD)--ATR_IA
        --OPEN CONNECTION
        loop1 = TRUE
        --connectted or not
            IF STATUS = 0 THEN
                 IF STATUS = 0 THEN
                            TMP_STR = 'RunJob'
                                IF  NOT UNINIT(ENTRY)THEN
                                    WRITE('---->',ENTRY,CR)
                                       WRITE('READING',CR)
                                        IF ENTRY <>0 THEN
                                            WRITE('>>>>>>',ENTRY,CR)
                                        ENDIF
                                ELSE
                                    WRITE('UNINITIALIZE DATA...',CR)
                             ENDIF
                    DELAY 6000
                    ENDWHILE
                        ELSE
                    loop1 = FALSE
                    CLOSE FILE ARCHIVO2
             ENDIF
          ENDIF
    END cont_msg
    Please put some light on the following:
    1- According to the KAREL manual(section 11.4.3), MSG_DISCO() is used for a closing socket if there is an error in file R/W operation or connection loss between server and client, i used it with byte_AHEAD() so python client can easily be connected again, but I got the following status code "Disconnect: 67208", what does this mean? Did I use this utility function in the right way?
    2- From where I can get the KAREL status code and their description?
    3- Do I need to call MSG_CONNECT() again after MSG_DISCO? i have tried this but got 67215.
    4-After receiving the data from the server, the python client closes the connection and BYTES_AHEAD() continuously called in the while loop and I notice for the first two iterations I got entry=0 and after that, I got data uninitialized warning on TP to avoid it I used UNITI() to close the connection. Why entry =0 for the first two loop iterations and an empty string after that?
    again many thatks
  • mahboobelahi93
    82
    • September 27, 2021 at 1:53 PM
    Thanks skyfire,
    i will try your option too. Is this is feasible for my task? from where i can get more information about it?
  • mahboobelahi93
    82
    • September 27, 2021 at 3:40 PM
    I modify the section inside the while like:
                    BYTES_AHEAD( ARCHIVO2, n_bytes,STATUS)
                    WRITE('>>>STATUS',STATUS,CR)
                    IF ((UNINIT (n_bytes)) AND (GATE)) THEN
                        GATE = FALSE
                        --WRITE('UNINITIALIZE DATA...',CR)
                        WRITE('DISCONNECTING SERVER...',CR)
                        WRITE('DONE. ',STATUS,CR)
                        --WRITE('STATUS',CR)
                    ELSE
                        IF (NOT UNINIT (n_bytes)) THEN
                            IF (n_bytes >= 1) THEN
                                WRITE('---->',n_bytes,'_bytes',CR)
                                WRITE('STATUS',STATUS,CR)
                                WRITE('READING',CR)
                                READ ARCHIVO2 (TMP_STR::n_bytes)
                                WRITE('Read status: ',STATUS,CR)
                            ENDIF
                            GATE=TRUE
                        ENDIF
                    ENDIF
                DELAY 1000
                ENDWHILE
    Here is the result:
    just able to hamdle Uninitialized data and client still does not able to connect server again
    SkyeFire
    1,052
    9,429
    • September 27, 2021 at 3:48 PM
    Thanks skyfire,
    It's detailed in the "Internet Options Manual," Section 6.3.6 "Running KAREL programs from the Web Browser." If you sign up for the Fanuc CRC support portal, you can access these manuals.
    There is a note that the robot must have R626, the "Web Server Enhancement" option, for this to work.
  • mahboobelahi93
    82
    • September 27, 2021 at 3:55 PM
    Quote from SkyeFire
    Thanks Skyfire,
    I checked and R626 is installed. I am in conversation with FANUC about purchasing R648 and R632.
    Do I exchange data (mentioned in one of the previous threads) between python clients and robots using this approach.?
    Any light on thread 6, please
    thanks
  • jmd2777
    34
    193
    • September 27, 2021 at 3:57 PM
    MSG_CONNECT() is a blocking function call. In other words, the program will not continue to the next line of code until a client attempts to connect. So the only time your client can connect is when the KAREL program is on the line MSG_CONNECT.
    So you need to either keep the connection open on the client side or run MSG_DISCO and MSG_CONNECT on the server every time and have the client reconect everytime.
    For the error codes, you need to look in the Error Code manual from Fanuc. It will show how to interpret the decimal error code. For error code 67208, the 67 is the Facility Code. In the manual you will find that 67 = HOST. The error number is 208. Now you can find the error in the manual as HOST-208 SM: Not Yet Connected.
  • mahboobelahi93
    82
    • September 27, 2021 at 4:00 PM
    Quote from jmd2777
    Thanks for JM for your response, let me try
    SkyeFire
    1,052
    9,429
    • September 27, 2021 at 4:09 PM
    • #11
    It worked for me. To be clear, I wasn't trying to do high-speed cyclic exchanges -- I think the fastest I ever ran it was to repeat every 250ms.
  • mahboobelahi93
    82
    • September 27, 2021 at 4:47 PM
    • #12
    Hi JM,
    Now client can join the server any time, thanks.
    I discover file must be closed before MSG_DICO() utility.
    I also notice that if the robot sends a message string using WRITE ARCHIVO2(TMP_STR) command and the client does not have any logic for receiving the server's message then READ ARCHIVO2 (TMP_STR1::n_bytes) operation is not successful and file_IO states generate the 2021 status code. What is the reason behind it? The client may be or may not be interested in messages from the server.
  • jmd2777
    34
    193
    • September 27, 2021 at 5:04 PM
    • #13
    I don't know.
    IO status codes can be found in the KAREL manual under the IO_STATUS command.
    2021 is "End of file for RAM disk device". I don't know what this means. Maybe that there was no data in the buffer?
    You can use "READ file_id(cr)" to clear IO_STATUS errors.
  • mahboobelahi93
    82
    • September 27, 2021 at 5:16 PM
    • #14
    Quote from jmd2777
    I don't know.
    Thanks,JM
    your so helpfull
  • mahboobelahi93
    82
    • September 30, 2021 at 3:13 PM
    • #15
    Quote from jmd2777
    hI JM,
    I found the following vision commands in the KAREL manual,
    1. V_FIND_VIEW
    2. V_RUN_FIND
    3. V_GET_PASSFL
    4. V_GET_OFFSET
    5. V_RUN_FIND
    6. V_SAVE_IMREG
    7. V_SNAP_VIEW
    I have written a vision-based pick place TP program for FANUC Educational Cell and it is working perfectly. All the above commands except "V_SAVE_IMREG" are being used in TP program directly or indirectly (buried under TP commands, see picture). How I can use the "V_SAVE_IMREG" command in the KAREL program just for getting the image data of the currently snapped picture as TP program handling everything? OR Should I write the whole vision routine in KAREL and call it from TP program?
  • jmd2777
    34
    193
    • September 30, 2021 at 4:06 PM
    • #16
    I don't have experience with iRVision in Karel.
    V_SAVE_IMREG may only be available in Karel. One option is to write a Karel program that only saves the image. Then you could keep your TP program and just add a call to your Karel program to save the image.
  • rf103
    17
    264
    • October 4, 2021 at 9:23 PM
    • #17
    This guy seems to have figured out how to do what Skyefire describes and wrap it in a software: https://github.com/gavanderhoorn/dominh
    The readme says you don't need any special options for it.
  • mahboobelahi93
    82
    • October 5, 2021 at 8:50 AM
    • #18
    Quote from rf103
    Hi RF,
    thanks for your comment, I am not sure whether this option is suitable for me or not as I need to handle image data, in addition, to remotely command the robot.
  • mahboobelahi93
    82
    • October 5, 2021 at 9:05 AM
    • #19
    Quote from jmd2777
    Hi JM,
    thanks for your support.
  • mahboobelahi93
    82
    • October 5, 2021 at 9:09 AM
    • #20
    Quote from SkyeFire
    Hi SkyeFire,
    Can you please give some detailed insights, how this HTTP communication is used in my case (just consider App) and how I can I send the required data from the robot to an external PC? Does it is possible to change Digital output or user output from python script?
Similar Threads
  • Keyence CV-X R30IB plus communication
    • Neilcrockett
    • July 29, 2021 at 2:26 AM
    • Fanuc Robot Forum
  • FANUC DeviceNet Communication with Delta PLC
    • shriraj lonkar
    • September 2, 2021 at 7:37 AM
    • Fanuc Robot Forum
  • Communication between Matlab and FANUC Roboguide
    • MatlabXFanuc
    • May 11, 2021 at 11:37 AM
    • Fanuc Robot Forum
  • Remote Start: Siemens PLC S1500 / Fanuc R30iB : Profinet Comm
    • MoEL
    • August 24, 2021 at 2:20 PM
    • Fanuc Robot Forum
  • OPC-UA Communication between FANUC robot and Allen-Bradley HMI (without PLC)
    • Jean-Fred B.
    • August 19, 2021 at 8:25 PM
    • Fanuc Robot Forum
  • FANUC Karel TCP Socket security
    • Milea Carmen
    • May 25, 2021 at 2:49 PM
    • Fanuc Robot Forum
  • PLC S7300 PROFIBUS COMMUNICATION WITH FANUC ROBOT
    • GIMM
    • May 13, 2021 at 4:50 PM
    • Fanuc Robot Forum
  • FANUC Robot - PC: Communication protocols
    • tboekhorst
    • October 27, 2020 at 6:28 PM
    • Fanuc Robot Forum
  • Communication between Schneider PLC and Fanuc robot
    • mathias drapier
    • May 16, 2019 at 9:09 AM
    • Fanuc Robot Forum
  • Python
  • socket
  • Socket Message
  • socket server
  • Karel programming
  • Position Register
  • LR mate200Di