  4. Kawasaki Robot Forum
Vacuum timeout Program
  • dodasch
  • November 7, 2023 at 10:57 AM
  • dodasch
    13
    Hey guys,
    Is there a possibility to query a signal state, as soon as it becomes HIGH, a timer of e.g. 20s should expire. After this time, the signal should be switched off.
    However, if the signal or another air output is activated again, the time should start counting from zero again.
    I have tried this in a pc.program:
    SOUT 2009 = 9 OR 10 OR 11 OR 12
    STIM 3010 = 2009, 20
    IF SIG (3010) THEN
    SIG -9,-10,-11,-12
    END
    My problem:
    the time is not reset if one of the signals mentioned is switched HIGH again in the meantime.
  • Go to Best Answer
  • Fubini November 7, 2023 at 12:38 PM
    Approved the thread.
  • dm.bogachev
    45
    87
    • November 7, 2023 at 1:35 PM
    Hi!
    If you need to switch off the same signals, consider PULSE instruction.
    And in your case, if condition goes right after the STIM command. It checks the signal once and then program goes further. You should use SWAIT command and then switch off the signals.
  • Alexandru
    49
    407
    • November 8, 2023 at 9:05 AM
    you can use TIMER or UTIMER function to scan the signals. For example:
    IF SIG(9) OR SIG(10) OR SIG(11) OR SIG(12) THEN
    SIGNAL 2001
    END
    IF SIG(-9) AND SIG(-10) AND SIG(-11) AND SIG(-12) THEN
    SIGNAL-2001
    END
    TIMER 7 = 0
    WHILE SIG(2001) THEN
    IF TIMER(7) > 20 THEN
    SIGNAL -9,-10,-11,-12,-2001
    END
    END
  • dodasch
    13
    • November 9, 2023 at 12:26 PM
    Quote from dm.bogachev
    Hi!
    This will only work in programs, but i would like to switch my vacuums also on my IF-Panel.
    So there is no option for a "MONITOR COMMAND" in which I can execute two commands.
    This also won't work:
    STIM 3009 = 9 OR 10 OR 11 OR 12, 20
    SOUT 2009 = 3009
    IF SIG (2009) THEN
    SIG -9,-10,-11,-12
    END
    because, the timer is not reset if one of the signals is switched on again in the meantime.
    The STIM function only works with one signal although it allows "AND" and "OR" :frowning_face:
  • dodasch
    13
    • November 9, 2023 at 12:35 PM
    Quote from Alexandru
    SIGNAL 2001
    END
    SIGNAL-2001
    END
    TIMER 7 = 0
    WHILE SIG(2001) THEN DO
    END
    END
    This example also do not work because:
    Quote
    My problem:
  • dm.bogachev
    45
    87
    • November 9, 2023 at 1:11 PM
    Quote from dodasch
    Consider using an autostart background program. You can add a button on your IFP with some internal signal and process it in background task. You also can add there some logic, which can reset TIMER as you want (Thanks Alexandru for idea). You can add in this background task (or made another) with something like. It will reset timer in Alexandru's code.
    .PROGRAM autostart2.pc()
        WHILE TRUE DO
            IF (SIG(9) OR SIG(10) OR SIG(11) OR SIG(12)) AND SIG(2001) THEN
                TIMER 7  = 0
            END
        END
    .END
  • kwakisaki
    694
    4,770
    • November 11, 2023 at 3:31 PM
    If you are using WHILE DO to execute a function within a PC Task (Not the WHILE TRUE DO as above).
    The rest of the PC Task will not be scanned/executed until the WHILE DO conditions are met.
    As a single function PC Task, then of course it is no problem.
    Below is an alternative example without WHILE DO for the function and includes IF panel data to display status of the outputs and toggle switches to activate/deactivate the outputs.
    It is not usually recommended to have buttons tied directly to outputs as these can be pressed during normal operation which may cause problems, so you should consider some conditions to prevent it.
  • dodasch
    13
    • November 15, 2023 at 8:33 AM
    Quote from kwakisaki
    Thanks for your detailed reply, but again:
    The main problem is, that the timer gets not reseted, as soon as one of the vacuum circuits is switched on again.
    This does the same as the code above:
    SOUT 2009 = 3009
    IF SIG (2009) THEN
    SIG -9,-10,-11,-12
    END
    I need something to intercept a signal edge, as soon as a signal switches HIGH, a flag should be set and the timer should start.
    If the signal remains HIGH, the time should still expire and the vacuum should switch off.
    BUT: As soon as another vacuum signal switches to HIGH, the timer should be reset.
    This prevents the vacuum from being switched off during operation.
  • dm.bogachev
    45
    87
    • November 15, 2023 at 8:53 AM
    Quote from dodasch
    I think that if you will remove the .mi.trigger == FALSE from kwakisaki's code, the timer will be resetted every time the signals become HIGH. Now, as I can see, .mi.trigger blocks the first IF condition (IF ((SIG(9)==TRUE.....) after the first time any of signals became HIGH (because .mi.trigger became FALSE again only after .tme.dly-0.1 or if all the signals are FALSE)
    So, if you need to reset timer EVERY TIME, THEN ANY OF SIGNALS are HIGH, then just remove (.mi. trigger == FALSE) part
    IF ((SIG(9)==TRUE) OR (SIG(10)==TRUE) OR (SIG(11)==TRUE) OR (SIG(12)) AND (.mi. trigger == FALSE) THEN
  • dodasch
    13
    • November 15, 2023 at 9:07 AM
    this will causing, that the timer won't reset. Because the Signal stays HIGH.
  • dm.bogachev
    45
    87
    • November 15, 2023 at 9:40 AM
    • #11
    Quote from dodasch
    Well, it will RESET timer every time, the signal stays HIGH, my fault
    But if you need some kind of rising edge, then try this. It's a bit bulky, but should work
    .INTER_PANEL_D
    1,4,1,"OFF     ON","",""," VACUUM 1",10,2,4,0,9,0
    2,4,1,"OFF     ON","",""," VACUUM 2",10,2,4,0,10,0
    3,4,1,"OFF     ON","",""," VACUUM 3",10,2,4,0,11,0
    4,4,1,"OFF     ON","",""," VACUUM 4",10,2,4,0,12,0
    15,9,1,4,9
    .END
    .INTER_PANEL_TITLE
    "",0
    "",0
    "",0
    "",0
    "",0
    "",0
    "",0
    "",0
    .END
    .INTER_PANEL_COLOR_D
    182,3,224,244,28,159,252,255,251,255,0,31,2,241,52,255,
    .END
      .tr1 = FALSE
      .tr2 = FALSE
      .tr3 = FALSE
      .tr4 = FALSE
      .tmr_max = 20
      TIMER 1 = 0
      WHILE TRUE DO
        IF SIG (9) OR SIG (10) OR SIG (11) OR SIG (12) THEN
          IF (SIG (9) AND .tr1 == FALSE) THEN
            .tr1 = TRUE
            TIMER 1  = 0
          END
          IF (SIG (10) AND .tr2 == FALSE) THEN
            .tr2 = TRUE
            TIMER 1  = 0
          END
          IF (SIG (11) AND .tr3 == FALSE) THEN
            .tr3 = TRUE
            TIMER 1  = 0
          END
          IF (SIG (12) AND .tr4 == FALSE) THEN
            .tr4 = TRUE
            TIMER 1  = 0
          END
        END
        IF SIG(-9) THEN
          .tr1 = FALSE
        END
        IF SIG(-10) THEN
          .tr2 = FALSE
        END
        IF SIG(-11) THEN
          .tr3 = FALSE
        END
        IF SIG(-12) THEN
          .tr4 = FALSE
        END
        IF TIMER(1) < .tmr_max AND (SIG(9) OR SIG(10) OR SIG(11) OR SIG(12)) THEN
          IFPWPRINT 1 = "Time left: " + $ENCODE(.tmr_max-TIMER(1)) + " s"
        ELSE
          SIGNAL -9, -10, -11, -12
          IFPWPRINT 1 = " "
        END
      END
    .END
    Edited 2 times, last by dm.bogachev (November 15, 2023 at 9:55 AM).
  • dodasch
    13
    • November 15, 2023 at 10:25 AM
    • #12
    Your example works!
    I think there is no way around setting a flag on a rising edge to reset the timer when vacuum signals are set again.
    Thank you! :red_heart:
  • dm.bogachev
    45
    87
    • November 15, 2023 at 10:41 AM
    • #13
    I'm glad that my code helped you!
  • kwakisaki
    694
    4,770
    • November 16, 2023 at 12:55 PM
    • Best Answer
    • #14
    Quote from dodasch
    Incorrect.
    You can utilize the SFLP command for this purpose as well as other methods of detection.
    If you had clearly identified your intentions from the start instead of providing ambiguous information like the following:
    Quote from dodasch
    This is what my initial example solved.
    There is no mention of whilst an output is HIGH if another output becomes HIGH.
    Your initial statement suggests AFTER completion if another output is activated again.
    The attached video displays a revised solution using SFLP command, CASE and PULSE commands.
    Files
    Untitled 1266.mp4 1.39 MB – 3 Downloads
  • dodasch
    13
    • November 20, 2023 at 8:44 AM
    • #15
    Incorrect.
    It's a bit intermediate to understand but this code works better than the code from dm.bogachev above!
    The code from dm.bogachev has an overlap with the timer somewhere.
    Sometimes the vacuum is simply switched off or you have problems switching it on because you have to press the interface panel button twice.
    Thank you for your reply and I apologize if I have not expressed myself correctly
  • kwakisaki
    694
    4,770
    • November 20, 2023 at 12:00 PM
    • #16
    Quote from dodasch
    Nothing intermediate at all, that's AS language right there in the same language dm.bogachev is using.
    May be you are referring to structure and commands, ease of reading, ease of execution etc.
    It is just an example remember, if it was something I was going to deploy onto a system, it would be written very differently.
    That's what makes AS sooo powerful and flexible, there is no 'text book' method or document on how you program an application.
    You have a book of commands (just like a toolbox full of tools), sometimes we use an alternative tool instead of using the correct tool to accomplish the same thing.
    This is why it is better to be 100% transparent about your application when it comes to Kawasaki and using Robot Forum, many examples, many solutions exist so it is definitely worthwhile grabbing a beer, crunching the manual and if you have it (KRoset), start key bashing and just see what you can achieve.
    I'm sure you'll be pleasantly surprised.
  • dodasch
    13
    • November 20, 2023 at 12:59 PM
    • #17
    The code is just a bit difficult for me to read because I'm not familiar with some of the tools, such as the SFLP command.
    But it's true, AS language is powerful, precisely because it's easier to reach your goal with the individual tools than with conventional programming languages. But you have to know when to use the right tools.
    I'm also not always sure whether I've chosen the easiest way or whether the code could be written even shorter.
    The forum is perfect for that, thanks for your help!
  • kwakisaki
    694
    4,770
    • November 20, 2023 at 1:37 PM
    • #18
    Quote from dodasch
    You know what I'm going to say already - as I stated it in my last:
    Your comment below I hear ALL the time:
    Quote from dodasch
    This shouldn't be a factor.
    - The right way is when your program works to the specifications required 100% of the time.
    - The wrong way is when your program doesn't work at all or only works a % of the time.
    So I'll ask two very simple questions:
    1. What do you mean when you say easiest?
    2. What would you accomplish by making code shorter?
    Ever heard of KISS.
    Adopt this direction from the start and you'll never fail.
    Try to run before you can walk will result in you falling over time and time again.
Similar Threads
  • Can not find debugger. How to single-step from the PC ? How about breakpoints ?
    • robotreto
    • May 22, 2023 at 11:40 AM
    • Kawasaki Robot Forum
  • Handshake with PLC and behaviour after UALM
    • OpaBroesel
    • April 19, 2023 at 1:23 PM
    • Fanuc Robot Forum
  • Robot part pick issues
    • AY_Robot
    • July 27, 2022 at 1:48 PM
    • Fanuc Robot Forum
  • Signal
  • vacuum
  • timeout
  • sout
  • stim