Auto reset $DMAURST not working
  • DS186
  • October 26, 2022 at 6:23 PM
  • DS186
    200
    1,072
    Hey guys,
    I have a new R-30iB Mate Plus controller and setting $DMAURST to TRUE is not working. The behavior is the same as with the variable set to FALSE.
    The software version is V9.40P/33 and this is the first time the auto reset is not working. It works with all my other robots with software versions <V9.40.
    Did somebody encounter the same behavior?
  • Welding Panda
    35
    • November 3, 2022 at 2:05 PM
    I have experienced the same thing before.
    I never found the reason though... Restart solved it for me.
  • DS186
    200
    1,072
    • November 7, 2022 at 10:28 PM
    Unfortunately that didn't help. When I am back on the robot I will try an init start.
  • pdl
    269
    1,533
    • November 8, 2022 at 12:11 AM
    You do know that will completely wipe the robot, correct?
  • DS186
    200
    1,072
    • November 8, 2022 at 9:56 AM
    Yes, I am aware of that. But thanks anyway for your hint.
  • DS186
    200
    1,072
    • November 15, 2022 at 11:51 AM
    I found the solution. There is a new DCS parameter called "TP Enabling Dev Reset" which secures the $DMAURST variable. I guess it was introduced from software version V9.40. Unfortunately, it is not described in the DCS manual. I have checked the latest version available on the FANUC portal.
    When changing TP Enabling Dev Reset to ENABLE then $DMAURST automatically also changes to TRUE. After applying the DCS parameters everything worked as expected.
    It is a bit odd because I applied some changes in DCS before but $DMAURST still didn't work. After setting TP Enabling Dev Reset back to DISABLE > Apply > Power cycle > TP Enabling Dev Reset ENABLE > Apply > Power cycle it worked.
    Images
      • 324.46 kB
      • 1,600 × 1,200
      • 42
  • Welding Panda
    35
    • November 15, 2022 at 5:00 PM
    Super info thanks!
    I will check on our machine. I was applying some DCS paramters, but I don't think I changed this.
  • DS186
    200
    1,072
    • November 15, 2022 at 5:17 PM
    Changing $DMAURST will automatically affect the value of TP Enabling Dev Reset (and vice versa) and requires to apply the changes of the DCS parameters. This didn't work for me for some reason and I only got it to work with the described procedure.