Hello guys, I have an error code refering to Dc-link type ( 38300 )in a S4C+ M2000 , does anyone know what it means ,attach photo ,thanks
S4C+ error Dc-link
-
Enio -
April 24, 2021 at 6:52 AM -
Thread is Unresolved
-
-
Just like the screen says, the DSQC358G DC-Link (rectifier) specified in the parameters is not found. We can assume the axis computer is not reading the type bits since it returned a zero. Make sure the DC-Link installed matches the parameters first. Try reseating the RJ45 connector second. Some of the RJ45 get brittle with age, seen a few fall apart. Used to carry a a few and a crimper back in the day.
-
Thank Skooter , we have try I-start in quiry mode and select Dc4 problem solved, but don't understand why loading with robinstall in silent mode doesn't recognize DSQC 358
-
Silent mode loads the defaults for the standard robot.
Query mode is where you enter non-standard variations such as a larger DC-Link or combo used when running ext. axes.
-
i looking for a translated list for S4 Rectifier
for example:
DSQC345A = DC0 = type code 16
i found this in the E-Drawings