Hello. Is it possible to connect E-stop signal from TP to an external system/controlling device? All im looking for is 24V signal from Estop.
Teachpendant e-stop to external system, DX100
- hublew31
- Thread is Unresolved
You can use internal signal for PROGRAMMING PENDANT EMERGENCY STOP signal, the signal for it is #80026. status of #80026 when the EMG key is not pressed is 1 and when the EMG press, this signal be 0.
you connect this signal to External signal of robot and connect robot external signal to your device.
for example:
STR #80026
OUT #30030
in this example the EMG signals is connected to #30030, when is not press, the #30030 is ON, when EMG press, the #30030 be OFF.
You can connect #30030 signal (that is external signal) to your devices.
Ok, thank you:))
Where do I do the:
«STR#80026
OUT#30050»
You must go to IN/OUT menu and select ladder editor but if you don't have its knowledge please don't modify, also for more knowledge see Concurrent I/O manual. It explain about ladder edit.
I’ve looked into the Concurrent I/O manual and tried to insert instruction but it won’t let me do anythig in ladder program. I am in management mode and user ladder...
What do you mean it won't let me do anything?
Are you in Teach?
You said you are in Management and in the user ladder.
When you press the SELECT key what happens? The Instruction list should show up.
Can you put the instructions in?
Did you compile it?
Did you verify that the address you were using as an output is not being used anywhere else?
Do you get an error when doing any of this? If so, what error number and text?
Yes Im in teach, when i press select nothing happens. So I cant even put the instruction in the ladder program
Are you sure you are in USER ladder?
Go to DISPLAY menu in ladder, there are two item, SYSTEM LADDER and USER LADDER,
Select USER LADDER.
It is better to go END line for insert new instruction, go to EDIT menu and press END LINE, it go to END , press SELECT key on the pendant a list of instructions appear.
Now you can select each instruction that you need.
Here is a video of me trying to do everything you told me to do.
Looks like you are doing everything correctly. Someone, then, has probably turned a parameter on to prevent editing of the ladder.
Right... Do you know which parameter has to be edited? I am trying to find a list of parameters for DX100, but no success so far.