This is how it looks like from my side. Photo was taken before changes. Now after 3 checks im 100% sure that all cables are correct. Major problem now is that I have error "EMERGENCY SHUTDOWN" "EXTERNAL EMERGENCY SHUTDOWN" "Illegal operating mode (?)"
"Safety / Gate Open" KRC2 in AUT mode
-
merbb -
October 16, 2020 at 10:27 AM -
Thread is Unresolved
-
-
error "EMERGENCY SHUTDOWN" "EXTERNAL EMERGENCY SHUTDOWN" "Illegal operating mode (?)" - messages in english - I have polish version.
Cant switch between operating modes
-
i don't see anything on 19
this is how jumper plug for KRC2 looks like
you can change language to English so we can read the messages
-
One thing I have seen ad hoc: you have connected 88 to 89 and 106 to 107, so may be you have blown a fuse.
May be you should contact a person that's used to handle with schematics and electric equipment. jm2c.
-
i don't see anything on 19
this is how jumper plug for KRC2 looks like
you can change language to English so we can read the messages
Translation : error "EMERGENCY SHUTDOWN" "EXTERNAL EMERGENCY SHUTDOWN" "Illegal operating mode (?)" - messages in english - I have polish version.
Cant switch between operating modes
This is how my jumper looks like. I dont see 4 pins there maybe this is the problem.
-
i don't see anything on 19
I made photos before realising that I connected it wrongly. Now everything is connected like on electric diagram. Errors are still the same...
-
One thing I have seen ad hoc: you have connected 88 to 89 and 106 to 107, so may be you have blown a fuse.
May be you should contact a person that's used to handle with schematics and electric equipment. jm2c.
Electric guy did that mistake. When I checked after him I found that mistake. Can you explain me where I can find that fuse?
Found this in PDF.
-
you don't have Polish version, you have all versions, Polish is what is currently displayed and it takes 2 seconds to change, no reboot required.
this is English forum, please make sure everything you post (screenshots too) are in English or choose suitable subforum in language of your choice.
your jumper plug looks ok, missing 4 pins are fine. that is EStop circuit and if it is connected 1-4 and 19-22, cabinet EStop button is bypassed.
note power jumpers you had ware wrong so as mentioned you must have blown fuse.
jumper 37-40 is only if plug also used for KRC1
-
The fuse was blown. After connecting my X11 all messeges dissapeared. So we have problem out of KRC2. I think problem is with FAULT on PILZ.
-
The easiest way will be to use the PILZ configuration software and have a look into the state of the PILZ, if it is a m0p as labeled in the schematic. This can be done without having the original source and without the password, but you need the software from PILZ, which is not for free (iirc).
All other attempts are like looking into a crystal sphere .
-
Finally. Pilz was broken inside and made that "SAFETY GATE OPEN"
-