Advertising
Having an issue with Creating a HOME_RETURN PROGRAM with Multiple JMP LBL's.
  • HOME RETURN
    1: OVERRIDE=50%
    2: IF VO[7]=ON, JMP LBL [10]
    3: PR[20]=LPOS
    4: R[10: CURRENT X]=PR[20,1:Curpos]
    5:____
    6: R[11: CURRENT X]=PR[20,2:Curpos]
    7: PR[20,3:Curpos]=450 MAY HAVE TO CHANGE UPPER OR LOWER.
    8:L PR[20:Curpos] 200mm/sec FINE
    9: IF R[11:CURRENT Y]>0,JMP LBL[1]
    10:L PR[12: Home_ret2] 200mm/sec CNT25 MAY HAVE TO CHANGE PR[12] TO ANOTHER PR WITH A SAFE PATH HOME.
    11: LBL[1]
    12: IF R[10: CURRENT X]>1800,JMP LBL[3] MAY HAVE TO CHANGE TO >1800 AND TEST OPERATION WITH ABORT ALL AROUND THE CELL IN ALL PROGRAMS.
    13: JMP LBL[3]
    14:L PR[31: Home_SAFE_HOME2] 200mm/sec CNT25 MAY HAVE TO CHANGE PR[11] TO ANOTHER PR WITH A SAFE PATH HOME.
    PR[33:SAFE_HOME4] 200mm/sec CNT25
    P[1] 400mm/sec CNT50
    15: LBL [3]
    16:L PR[1: HOME POSITION] 200mm/sec FINE
    LBL[10]
    18:__
    19:__
    20:__
    [END]
    Change 12: IF R[10: CURRENT X] to >1800 instead of Less than 1800 8/14/19 11:20AM
    Note: This program works as planned while the robot is in the Furnace area but anywhere else in the cell it has Limit faults.
    Is there an option if to add multiple JMP LBL's in the same line?
    Any support is appreciated.
    Thank You
    SRTAutomation.
  • I'm not really sure what you mean about adding multiple JMP LBLs in the same line. A JMP LBL is basically a GOTO statement; you can't jump to two places at once.
    Line 12 is completely irrelevant to your program; if your logic on line 12 is true then line 12 jumps to lbl[3], if it's false then you jump to lbl[3] on line 13. Either way, nothing between line 13 and lbl[3] will be executed.
    As far as having limit faults trying to go home, generally you'll want to do a linear move to safely clear the workpiece and then a joint move for the move home.
  • On lines 12 and 13 I noticed that they both have JMP LBL [3]. So whether it is greater than 1800 or not it won't matter because either way it is jumping to label 3 and skipping line 14. I would assume this could have something to do with why you're hitting limit faults because no matter what you're jumping to line 15 and 16 moving to PR1 without ever executing line 14.
    EDIT* I typed this out a little over an hour ago and got called off to fix something and just came back and hit send. I didn't see where TitusLepic had already pointed out the mistake.
    "I could tell that my parents hated me. My bath toys were a toaster and a radio."
    I'm wondering if line 14 is an intermediate move to get to a safe position to then move to PR1 and since it is never executed the robot tries to move straight to PR1 resulting in the limit error.
  • Thanks for the feedback.
    Some Details about the Robot cell:
    Foundry Robot R-2000iB 210F-
    The Robot EOAT is a square shaped Ladle that dips Molten Aluminium.
    Auto pours into 3 tilt casting machines.
    Last month on 2nd shift the robot crashed into the furnace divider and busted the ladle into pieces.
    Crashes have happened before and the robot crashed into the light curtain at Machine 1.
    This was due to MAINT pressing Abort all and then pressing cycle start on the HMI.
    The 1st call program in MAIN is PR[1:HOME POSITION] so the robot took the shortcut back home- Causing Chaos!
    The HOME_RETURN program is a call program that will be in the 1st line of MAIN.
    So anywhere in the cell if Abort all is pressed the Robot will return home without spilling hot metal, crashing, or limit faults.
    Thanks for the FEEDBACK!
    srtautomation
  • So you need the home_return program to figure out where the robot is in 3D space, move a safe direction/distance to clear any obstacles, and then go home without hitting a limit.
    I've never used DCS, but if I understand it right from what I've read, you can set up 3d zones in your cell that will turn on an output when the robot is in that particular area. If you have DCS I think that would be the easiest way, just check what output is on and call the appropriate motion to clear your obstacles.
    You can also do what you're doing now; grab the the LPOS x, y, and z and use lots of conditional branching to determine what home path to call
    The third way is to use a register in your main program and update the value as the robot moves to different areas. For example
    R[1] = 0
    move somewhere
    R[1]=1
    move some other place
    R[2]=2
    etc
    then use a SELECT statement at the beginning of the home_return program to call the right homing routine
    SELECT R[1] = 0 JMP LBL[1]
    =1 JMP LBL[2]
    =2 JMP LBL[3]
    ELSE JMP LBL[4]
  • I would be having a talk with your maintenance department for sure! But as TitusLepic suggested using data registers is a great way to prevent this. Another idea would be to also make the move to home a little slower and call a collision adjust right before hand so if there is a mishap it won't cause much, if any damage. You can always readjust the collision detect immediately after it is home.
    To add, for a temporary quick fix while you work on the other program changes you could always add in a line at the top of the main program to wait until the "At Perch" output is on before executing the main job. That'll force them to take the robot home manually before being restarted after an abort all and give you a bit of "peace of mind" while you work to correct the issue permanently.
    Edited once, last by SHIFT_Lock ().
  • This was due to MAINT pressing Abort all and then pressing cycle start on the HMI.
    I've had this issue before and it is no fun. I did the same things motioned above: LPOS and monitor DCS and/or reference positions to figure out where in space the robot is and how to get it home.
    On one installation with 4 motion groups in a rotisserie setup:
    1. The operator needs to get the robot or other axes home after an e-stop condition or something else that left them in a place other than home
    2. Abort all is required. This is done to prevent the HOME program from running (or possibly running) every time the loop restarts as this cell is pretty complicated.
    4. The operator presses a button on an HMI screen to run the HOME program
    4. Monitoring UOPS (if I remember correctly) will show that the robot has been aborted and will allow the HOME program to execute
    5. Monitoring system variables, if the robot has been jogged by a human since the last motion instruction, the HOME program will end and display a screen that says the robot or another axis has been jogged and will have to be moved home manually. This is done to get the robot home from a general area where we can expect the robot to be during normal operations. I was unable to account for all the possibilities the robot may have been jogged to. The other 3 motion groups were rotary and fairly easy to get home.
    6. Operators and maintenance are instructed to never jog anything on this cell unless they have tried to abort and run the home program. One of the very few times an abort all is encouraged.
    Hope this helps...
  • 11:45AM Checked The Robot Reference position and noticed at home position in the programs and PR[1: HOME POSITION]
    Neither DO[8: AT HOME] or VO[7: At Perch] was on Keep in mind this is a refurbished robot and was recently installed.
    The home position had to be touched up a few weeks ago to a better location out of the furnace +Z:
    Recorded the reference position and both DO[8] & VO[7:] are on now.
    Also I was checking the DCS zones before lunch break and there is collision guard that I set to 130% but no DCS to be found- May have to get a firmware update.
    Shift_Lock I will add WAIT VO[7: AT Perch] in the 1st line of MAIN until the HOME_RETURN PROGRAM has been tested and finalized.
    Thanks for the Johnny INPUT ALL!
    srtautomation
  • You don't necessarily need DCS zones set up to adjust the collision detect within a job. Add in a line before it calls the move home such as "COL GUARD ADJUST 130" and it will adjust it on the fly. Just know that your payload settings must be properly setup or this will just cause issues for you. But you can do this anywhere in the program so if you want to decrease the sensitivity after it's home write it back in as "COL GUARD ADJUST 100" which is default or whatever it is you want it at.
  • I have used the register method to get home, and it works pretty well. There are some gotchas though:
    * if you jog the robot, the register will be rendered invalid -- this is where monitoring the system variables comes in handy
    * you have to make sure if you execute a motion instruction in teach mode, that you execute the register set instruction as well, or the home job will likely not do what you intended.
    I haven't tried this, but a way to address the second issue is to use the DB tag in your motions, for example:
    L PR[1] 50% CNT100 DB 0.0mm, POINT_LOGIC
    R[1] = 1
    The DB stands for "distance before", and setting this to 0 means perform the action when the robot reaches the position--not sure how this works with CNTx motion though.
    POINT_LOGIC is a way to insert instructions inline.
  • I use J1 Like this:
    ! turned toward outbound conveyor
    if R[20:Jpos1] > 120 Jmp Lbl [100]
    ! @ winder
    if R[20:Jpos1] > 90 Jmp Lbl [200]
    ! @ buffer conveyor
    if R[20:Jpos1] > 0 Jmp Lbl [300]
    ! @ Pick pallet
    if R[20:Jpos1] > -45 Jmp Lbl [400]
    ! Not sure where I am. Job me please!
    Ualm[2]
    Lbl [100:@ outbound cnvr]
    if R[32:LposZ] < 120 Jmp Lbl [150] or what ever checks are needed for that area
    PR[30:Lpos,3] = 120 Often normalize Z to a point that will clear area
    J PR[30:Lpos] 4000mm/s CNT 25
    Lbl [150]
    j PR[1:Home] 4000mm/s Fine
    Jmp Lbl [999]
    Lbl[200:@ Winder]
    ETC... Different checks for each area
    Jmp Lbl [999]
    ETC...
    Lbl[999:Done]
    I had argued with PLC guys, project manager,electrician, etc (Basically everybody that has no clue about robots) that this "Home return" function is ONLY when the robot is in auto mode. Once the pendant goes into manual mode game is over, no buts....
    Therefore those gotchas should never ever happen
    somar