Not without details. What are you trying to communicate with? What hardware do you have? What Master and Slave devices? Is the cable run and terminated correctly? What is your bus topology?
This looks like the robot is configured to act as a PB Master to a large number of Slave devices. Where are they? How did you create the DATABASE_PATH file?
Not without details. What are you trying to communicate with? What hardware do you have? What Master and Slave devices? Is the cable run and terminated correctly? What is your bus topology?
This looks like the robot is configured to act as a PB Master to a large number of Slave devices. Where are they? How did you create the DATABASE_PATH file?
Did I create Pfbs and iosys files by counting too many modules when I had 1 i/o module? I didn't understand what you meant.
Sorry, I'm new to this stuff.
Did I create Pfbs and iosys files by counting too many modules when I had 1 i/o module? I didn't understand what you meant.
Sorry, I'm new to this stuff.
What is the hardware layout of your bus? Every Profibus Device connected to the robot: Which CP5614 port, what their PB addresses are.
Without knowing that IN FULL DETAIL, posting your .INI files is utterly worthless.
What is the hardware layout of your bus? Every Profibus Device connected to the robot: Which CP5614 port, what their PB addresses are.
Without knowing that IN FULL DETAIL, posting your .INI files is utterly worthless.
Hi,
The currently active link is as attached. I only made changes to the Auto external parameters, pfbs and iosys files on the robot. I specified the already existing ldb file in the pfbs file. I just found out that I need to generate the ldb file with the NCM PC manager program. I will do it now after this message. Do I have anything else?
Best Regards
Attached to the ET200 cabinet with the attached picture. Not connected to other modular cabinet. Picture of Et200 is above. I uninstalled the Profisafe module.. Picture of Et200 is above. I uninstalled the Profisafe module..
They said that Krc2 and profisafe do not communicate with profibus.
there is old ldb file. I didn't create a new one.
KRC2 D:\Internat\Bus\Profibus\NCM_PC
I wanted to look at the file path but there is no Internat folder.
The old file path to the drivers/FW_5613.bin file path. I didn't create a new one. I don't know how to create it.
You must get it somewhere else, or you can use Simatic Manager Step 7
that will never work...
ET200S is a SLAVE
X851 is SLAVE
slave to slave communication is impossible. there has to be a master present. you must use X850 instead of X851 in this case.
and the bus wiring need to be correct. and it is not.right now there is a length of cable between two nodes but the cable side at X851 is DISCONNECTED.
you MUST use A1/B1... ALWAYS. A2/B2 is used only when bus extends beyond current node and goes to the next one. and both ends need terminating resistor switched on