Profinet Configuartion KR6

  • iDio
  • February 6, 2018 at 1:43 PM
  • Thread is Resolved
  • iDio
    Trophies
    3
    Posts
    140
    • February 6, 2018 at 1:43 PM
    • #1

    Hello everyone! I've configured a Profinet configuration between PLC and a KR6 R900 sixx.
    Siemens S7-1200 as controller, KrC4 as device.

    The connection is okay ( profinet names and so on).
    I'm just missing the "I/Os mapping". How do i configure this? Or do I check the profinet signal inputs on the robot?

    Extra: The connection is open between robot and PLC. Do i need to add the PLC to workvisual project as well? The robot is the device, so I didn't do that..
    Thank you!

  • Mr.E
    Reactions Received
    1
    Trophies
    3
    Posts
    41
    • February 6, 2018 at 5:10 PM
    • #2

    You need to tell the robot how many I/O are for Profinet communication in your Profinet Communication Settings.

    Then go into 'IO Mapping' in WoV, on the left, select 'KRC I/Os' - 'Digital Inputs', on the right (under 'field busses' tab) select 'profinet Inputs', and connect the 2 wherever suits. Repeat for Outputs. Deploy project, job done.

    No Need to 'add PLC to WoV project'.

  • iDio
    Trophies
    3
    Posts
    140
    • February 6, 2018 at 8:32 PM
    • #3

    Yap. I did that and all good. But I still can't see any changes in the inputs/outputs display ( digital )..

  • fanucrobot_Dr
    Trophies
    3
    Posts
    11
    • February 6, 2018 at 10:39 PM
    • #4

    Double click Profinet under Bus structure in WoV and Make sure you have the device name added(PLC) under the Profinet - Device name....also number of safe IO's, number of IO's and Profinet Version is correct

  • iDio
    Trophies
    3
    Posts
    140
    • February 7, 2018 at 11:32 AM
    • #5
    Quote from fanucrobot_Dr


    Double click Profinet under Bus structure in WoV and Make sure you have the device name added(PLC) under the Profinet - Device name....also number of safe IO's, number of IO's and Profinet Version is correct

    -Device name and controller name under Profinet are correct : when i disconnect the cables the communication is closed ( and restored when connected )
    -Safe I/O's - none ( zero)
    -Number of I/Os: 8
    - KSS version 8.3.17 - Profinet version 3.2.0 - GSDML-V2.31-KUKA-KRC4-ProfiNet_3.2-20140908

    I think everything is okay.. right?

  • fanucrobot_Dr
    Trophies
    3
    Posts
    11
    • February 7, 2018 at 3:03 PM
    • #6

    The IO's depend on how your plc is configured, they have to match.
    Do you have any PNIO errors or could not connect to device showing on the teach pendant?

    The Kuka switch inside the controller cabinet needs to be configured on your network to allow communication between the PLC and the robot, make sure it does not have a red light

    I would also check to make sure your KLI (virtual network 5), under diagnostic, has the correct robot IP and the PLC also is using correct IP for the robot.
    The KLI network will also show if you are sending / receiving data

  • iDio
    Trophies
    3
    Posts
    140
    • February 7, 2018 at 3:24 PM
    • #7
    Quote from fanucrobot_Dr


    The IO's depend on how your plc is configured, they have to match.
    Do you have any PNIO errors or could not connect to device showing on the teach pendant?

    The Kuka switch inside the controller cabinet needs to be configured on your network to allow communication between the PLC and the robot, make sure it does not have a red light

    I would also check to make sure your KLI (virtual network 5), under diagnostic, has the correct robot IP and the PLC also is using correct IP for the robot.
    The KLI network will also show if you are sending / receiving data

    IO's, see attached.
    No PNIO errors. Connection ok ( IP is also correct - connected on KLI (X66) ). I go to Diagnostic Monitor on teach pendant and KLI is swapping information. ( TX and RX counters increasing).

    But in the Diagnostic Monitor - Profinet IO-Driver (PNIODriver) the Profinet Blink is OFF. Is it suppose to?

    Any ideas?

    Images

    • tia.png
      • 53.18 kB
      • 1,005 × 439
      • 33
    • wv.png
      • 101.67 kB
      • 1,926 × 827
      • 35

    Files

    tia.png_thumb 9.67 kB – 37 Downloads wv.png_thumb 6.79 kB – 37 Downloads
  • fanucrobot_Dr
    Trophies
    3
    Posts
    11
    • February 7, 2018 at 4:40 PM
    • #8

    It looks like, from the pictures, that your WoV configuration is correct. I would make sure the PLC is configured to the correct bit range.
    You can also reset / reconfigure IO driver by going to Display - Inputs/outputs - IO drivers

  • iDio
    Trophies
    3
    Posts
    140
    • February 7, 2018 at 5:02 PM
    • #9
    Quote from fanucrobot_Dr


    It looks like, from the pictures, that your WoV configuration is correct. I would make sure the PLC is configured to the correct bit range.
    You can also reset / reconfigure IO driver by going to Display - Inputs/outputs - IO drivers

    You mean this: ( see attached )

    Images

    • plc.png
      • 55.58 kB
      • 1,232 × 560
      • 33

    Files

    plc.png_thumb 9.52 kB – 37 Downloads
  • panic mode
    Reactions Received
    1,278
    Trophies
    11
    Posts
    13,076
    • February 7, 2018 at 5:44 PM
    • #10

    That shows only plc cpu... I see no network or KRC4...

    1) read pinned topic: READ FIRST...

    2) if you have an issue with robot, post question in the correct forum section... do NOT contact me directly

    3) read 1 and 2

  • iDio
    Trophies
    3
    Posts
    140
    • February 7, 2018 at 5:49 PM
    • #11
    Quote from panic mode


    That shows only plc cpu... I see no network or KRC4...

    See attached.

    Images

    • devices.png
      • 121.45 kB
      • 1,743 × 932
      • 33
    • kr.png
      • 96.75 kB
      • 1,731 × 880
      • 29

    Files

    devices.png_thumb 9.29 kB – 36 Downloads kr.png_thumb 8.46 kB – 36 Downloads
  • iDio
    Trophies
    3
    Posts
    140
    • February 8, 2018 at 5:46 PM
    • #12

    Problem solved. The I/O mapping in TIA Portal was wrong.. I was activating the output with address 0.0 (0.1,...) and it was suppose to be address 2.0 (2.1,..).
    Thank you all!

Advertising from our partners

IRBCAM
Robotics Channel
Robotics Training
Advertise in robotics
Advertise in Robotics
Advertise in Robotics

Job Postings

  • Anyware Robotics is hiring!

    yzhou377 February 23, 2025 at 4:54 AM
  • How to see your Job Posting (search or recruit) here in Robot-Forum.com

    Werner Hampel November 18, 2021 at 3:44 PM
Your browser does not support videos RoboDK Software for simulation and programming

Tag Cloud

  • abb
  • Backup
  • calibration
  • Communication
  • CRX
  • DCS
  • dx100
  • dx200
  • error
  • Ethernet
  • Ethernet IP
  • external axis
  • Fanuc
  • help
  • hmi
  • I/O
  • irc5
  • IRVIsion
  • karel
  • kawasaki
  • KRC2
  • KRC4
  • KRC 4
  • KRL
  • KUKA
  • motoman
  • Offset
  • PLC
  • PROFINET
  • Program
  • Programming
  • RAPID
  • robodk
  • roboguide
  • robot
  • robotstudio
  • RSI
  • safety
  • Siemens
  • simulation
  • SPEED
  • staubli
  • tcp
  • TCP/IP
  • teach pendant
  • vision
  • Welding
  • workvisual
  • yaskawa
  • YRC1000

Thread Tag Cloud

  • abb
  • Backup
  • calibration
  • Communication
  • CRX
  • DCS
  • dx100
  • dx200
  • error
  • Ethernet
  • Ethernet IP
  • external axis
  • Fanuc
  • help
  • hmi
  • I/O
  • irc5
  • IRVIsion
  • karel
  • kawasaki
  • KRC2
  • KRC4
  • KRC 4
  • KRL
  • KUKA
  • motoman
  • Offset
  • PLC
  • PROFINET
  • Program
  • Programming
  • RAPID
  • robodk
  • roboguide
  • robot
  • robotstudio
  • RSI
  • safety
  • Siemens
  • simulation
  • SPEED
  • staubli
  • tcp
  • TCP/IP
  • teach pendant
  • vision
  • Welding
  • workvisual
  • yaskawa
  • YRC1000
  1. Privacy Policy
  2. Legal Notice
Powered by WoltLab Suite™
As a registered Member:
* You will see no Google advertising
* You can translate posts into your local language
* You can ask questions or help the community with your knowledge
* You can thank the authors for their help
* You can receive notifications of replies or new topics on request
* We do not sell your data - we promise

JOIN OUR GREAT ROBOTICS COMMUNITY.
Don’t have an account yet? Register yourself now and be a part of our community!
Register Yourself Lost Password
Robotforum - Support and discussion community for industrial robots and cobots in the WSC-Connect App on Google Play
Robotforum - Support and discussion community for industrial robots and cobots in the WSC-Connect App on the App Store
Download