For example can someone explain me this configuration down?
What is the number 1 after INW then what is the 1 after = and what are numbers 2 and x1? and is there some calculator or how can i calculate this?
[DEVNET]
INW1=1, 2, x1
OUTW1=1, 0, x1
[DEVNET]
INW1=1, 2, x1
OUTW1=1, 0, x1
read bottom of IOSYS.INI, it explains format
INW1=1, 2, x1
INW1= KRC Address
1=Module address
2=Offset
x1=Length
INW1
IN - digital inputs
W - word (16 bits) this is the length (x1 on right side means you only need one word)
1 - KRC address starting at 8*X+1 where X is your number, in this case it is 1, so 8*1+1=9, 16 bits starting at input 9 (range 9-24)
I am not sure about last calculations, maybe in case of word you would use 16*X+1 to calculate KRC address (range 17-32)