Hello all,
Is it possible to have certain I/O turn off when the emergency stop button is hit? This is for an r-30ib controller with handling tool.
thanks!
Turn off certain I/O when emergency stop is activated
-
robot take over -
October 9, 2015 at 6:31 PM -
Closed -
Thread is marked as Resolved.
-
-
Yes, there are several ways of doing it. Are you needing outputs off for human safety or machine/process related reasons?
Sent from my VS985 4G using Tapatalk
-
I need the outputs off for machine/process related reasons. Just out of curiosity what would be different between the two?
-
The difference is that human safety should not be implemented programmatically, but by hardware circuits or at least by safety-rated programmable device (DCS in the robot or a safety PLC).
For process purposes you can use BG Logic. -
If you just want a specific DO to turn off, you can use the I/O Interconnect and link it to ES.
If you want several, use the ESPB1 & ESPB11 connection on TBOP14 to disconnect the supply voltage going to those outputs whenever the robot e-stop buttons are pressed. Be aware that the relay is also open whenever the controller is off. -
If you just want a specific DO to turn off, you can use the I/O Interconnect and link it to ES.
There are two EStop buttons- on the TP and on the controller, and both cannot be mapped to the same DO by Interconnect. -
Under the config menu you can set a single output to go high if any e-stop occurs, then you can tie that on to whatever outputs you want to turn off via background program or in your plc.
-
What abt RO? Instead of DO
-
You can use any signal in BGlogic.
This thread is 5 years old. If have a new question then start a new thread.
-