We have irb1400 with s4cplus controller , when I power on system does not start and teachpendat says that " teachpendant comminucation lost" . what cause can be this error? It can be electrical problem or software problem ? To make sure that it is not software problem , i want to reinstall system again .
Can I make it without teachpendant ?
thanks for advance...
How to reinstall system without teachpendant at s4cplus
-
m.otcu41 -
May 11, 2014 at 11:05 AM -
Thread is marked as Resolved.
-
-
Hello,
You can use Ethernet connection on S4C+, and use RobInstall software. I believe you don't need the TPU during installation.
By the way, maybe you can check your TPU cable and plugs that could be defect?
-
thanks Sir,
I controlled the teachpendant cable and connectors , it is not broken
Will I use this ip address " 192.168.125.1 " or each conroller has special ip address?
best regrets -
I'm not really used with that but per default, I believe it's the same address except if you set up a network with some robots.
-
When using the service port you need to configure your computer to the following IP settings. The service port is the port on the IO computer board and or the port on the front of the controller
192.168.125.82
255.255.255.240 subnet
192.168.125.81 GatewayAccess the main flash at
192.168.125.1
-
By installing robot ware in side of robot controller you can erase tech pendent communication fault ,but some time you have to check the heat sing CPU of mother board ,you can use silicon between heat sing and CPU’s surface .
-
you can use the software WSFTP
-
I also had the teach pendant comunication lost error and it turned out to be a defective power supply.
-
thanks everyone for help ,
I solved the problem, i had a problem at my robot because it can not read the HDD , I changed the flashdisk and solved problem