hi dears
please help me
in gave 3HAC2700-2 DISC(1) and inseted it after key disk
after 1 minute teach pendant told me please wait and do not turn off
i wait for 30 minutes and i saw nothing
then i turn off controller .
now when i turn on robot its write start up progressing and counting a timer.....
and it doesnt go next step
plese help meeeeeeeeee
robot waiting in progress but nothing (Solved)
-
ebb -
October 15, 2013 at 8:55 AM -
Thread is marked as Resolved.
-
-
The robot didn't ask you about key disc again?
Try remove de battery and CPU boards and put it again.
I hope that you have the board DSQC 373, because system 3HAC2700-2 is only can be use on it.
-
thanks for your answer
no it dosent ask key disk
its stopped in start up processing step
I remove cpu and battery but i still have that problem
last week i insert key disk then i insert a boot disk , suddenly every things stopped.
now i have a red led in cpu and memory
thanks for your attention -
ok!
Did you double check if you are using the robot computer DSQC373 or other?If you don't have the DSQC373 the problem can be the robot computer because the system 3.2 make an overflow in the flash memory on the robot computer and it will need to be repaired.
But if you are using DSQC373 then the Leds that you said show us about a situation, when the robot turn on the led goes on and immediately goes off, if the led goes on again an error was detected in the test. How are the leds working when turn on the system?
The robot computer is the first unit to start after a cold/warm start.
Do you have another CPU boards and Teach pendant ?
-
thanks so much for your reply
i checked it
robot computer DSQ363
memory extention DSQ317
main computer DSQ325all leds of the boards is red , as soon as i turn it on.
thanks for your attention -
In this case your problem probably is the robot computer DSQC363.
You need to repair it.
The appropriate system in your case is the baseware 3.0 (3HAC2390).
Where's you from?
-
thanks
you help me alot -
is there anybody that know how can i fix it?
-
"NOTE:
Compatibility:
DSQC363 (Robot Computer) is NOT supported in RW3.2. If cold booting with RW3.2, there
will be an overflow in the flash memory on the robot computer, and a special tool at the
supplier is needed to recover the flash. Ensurethere is a DSQC 373 (Robot Computer) installed
in the Robot Controller before starting to boot 3.2."In your case you need to repair it. You have 2 options, send the board to ABB repair departement OR send the board to a company supply eletronic services on robot boards. If you are in Brazil I can help you.
-
"NOTE:
Compatibility:
DSQC363 (Robot Computer) is NOT supported in RW3.2. If cold booting with RW3.2, there
will be an overflow in the flash memory on the robot computer, and a special tool at the
supplier is needed to recover the flash. Ensurethere is a DSQC 373 (Robot Computer) installed
in the Robot Controller before starting to boot 3.2."In your case you need to repair it. You have 2 options, send the board to ABB repair departement OR send the board to a company supply eletronic services on robot boards. If you are in Brazil I can help you.
its not possible to repair it by my own?
its very important for me.
if i have flash program and programer schematic i think i can repair it.
thanks for your attention. -
Sometimes PS can creat this problem. It needs to be replaced with a new one.
Regards,
http://www.robottr.com -
Also try to replace the flash drive from the MAIN Computer Unit.
-
Hi,
I have already repaired three cards DSQC363. There are that re-load the flash memory chips. There are that unsolder and re-weld.
Regards
(Sorry, my english is very bad) -
I did not solve this problem
if any body have some solution please tell me -
Perhaps an update is in order - which of the suggestions have you tried.
-
thanks for your help
And special thanks from MR.Lanisoft.I solve this problem.
I take out flash chipsets in DSQC363 and Re_load those and
Re_solder it.
Its ok now.....I need disket of Program number 3HAC1462-1
can any body gave me it?
I have this message:please insert disk (1) in disk set
with label: programNO3HAC1462-1
and press any key to start loading. -
when you say "re-load" what do you mean?
to erase the chips?regards
-
My assumption is that it means to erase the flash, reinstall on the board, and then let the software update the flash when you reload software.
The other assumption would be removing the flash from a good board running the same revision software, copy the flash, and load the copy in the flash for another board of the same type.
All this requires an IC programmer capable of read/write for the particular flash IC and very good solder/desolder equipment along with the knowledge and skill to use it. -
thanks for your help
And special thanks from MR.Lanisoft.I solve this problem.
I take out flash chipsets in DSQC363 and Re_load those and
Re_solder it.
Its ok now.....I need disket of Program number 3HAC1462-1
can any body gave me it?
I have this message:please insert disk (1) in disk set
with label: programNO3HAC1462-1
and press any key to start loading.Hi, which chips are flash-chips that must be reloaded? Am29F800B? There are two of them?