QuoteQ6 how is the IO mapping done on the robot side? Right now i have a cell that is duplicate of previous one. Robots talk to AB PLC over EthernetIP and while fieldbus is working, list of signals is not the same as on robots from previous cell. for example mode selection switch status used to be seen by PLC in the last three bits of byte0, now it is in byte4, job number is moved 2 bytes etc. of course we would like to see all cells use same mapping (and PLC program).
I suppose the EXTERNAL IO ALLOCATION on the Ethernet card doesn't correspond with Concurrent IO (CIOPRG.LST file).
Chapter 4.2 Setup Procedure of this manual Ethernet function manual describes setting up Ethernet card procedure in Maintenance Mode. (You may be asked by server to leave contact details, before it allows you to download/read pdf file)
Concurrent I/O manual is another one which explains how to modify CIO.PRG file to your needs.
btw. You double use Q10 number.