Hello all. I am working on my project offline (no PLC connected and I/O mapped to it) and I have a DI that is status-ON all the time. I go to simulate and turn it off however, as soon as I unsimulate, it goes right back to ON. All of my other DI's have the expected status of OFF. I checked the details of this input and it is identical to the others. Any idea why this is behaving like this? Thank you
DI in an odd state whilst offline
-
ceilingwalker -
August 2, 2023 at 9:37 PM -
Thread is Unresolved
-
-
How is it configured? Are there any interconnections set up?
-
How is it configured? Are there any interconnections set up?
None of my DI's are interconnected. I only have one RO interconnection.
-
Is there a wire connected to the input ?
-
How is it configured?
-
How is it configured? Are there any interconnections set up?
The correct answer is no, I do not have any interconnections set up.
-
Is there a wire connected to the input ?
No, it's only in RoboGuide. I am not connected to the robot or any other h-ware.
-
Screenshot 2023-08-02 142714.pngHow is it configured?
Identical to the others.
-
Do you have anything else configured to use rack 89 slot 1 that may overlap with the range? Maybe the UOP?
-
Is it set to inverse polarity? (next > detail)
-
Is it set to inverse polarity? (next > detail)
Negative, it's on "normal". That was the first thing I checked.
-
Do you have anything else configured to use rack 89 slot 1 that may overlap with the range? Maybe the UOP?
Negative. I have done that accidentally before and the software yells at me when I do it. Lol
-
This is really strange but........I performed a cold start and that resolved it. Thanks for your input.