    Hi guys,
    I am trying to run the switch statement but getting EWorkToolSwitch value invalid message when stepping through. Can someone tell me what am I doing wrong here?
    FYI: WorkToolEnum defined at config.dat file this way
    "ENUM WorkToolEnum GetScrapTool,GetScrewTool,GetStapleTool,GetNailTool,LeaveScrapTool,LeaveScrewTool,LeaveStapleTool,LeaveCurrentTool,LeaveNailTool"
    Code:
    &ACCESS RVP
    &REL 834
    &PARAM DISKPATH = KRC:\R1\UserPrograms
    DEF  ToolChange (eWorkToolSwitch:IN )
    DECL WorkToolEnum eWorkToolSwitch
       ;FOLD INI;%{PE}
          ;FOLD BASISTECH INI
             GLOBAL INTERRUPT DECL 3 WHEN $STOPMESS==TRUE DO IR_STOPM ( )
             INTERRUPT ON 3
             BAS (#INITMOV,0 )
          ;ENDFOLD (BASISTECH INI)
          ;FOLD USER INI
             ;Make your modifications here
          ;ENDFOLD (USER INI)
       ;ENDFOLD (INI)
    GoHome()
    SWITCH eWorkToolSwitch
      CASE #GetScrapTool
           ;CHECK IF THERE IS ANY TOOL PRESSENT AT TCU
           IF diScrewToolContact == TRUE THEN
              LeaveScrewTool()
           ENDIF
           IF diStapleToolContact == TRUE THEN
              LeaveStapleTool()
           ENDIF
           IF diNailToolContact == TRUE THEN
              LeaveNailTool()
           ENDIF
           ;TO PLC: ALARM TOOL MISSING
           WHILE (diScrapToolContact == FALSE) AND (bAllToolsDocked == FALSE)
                 Alarm(141)
           ENDWHILE
           ;CHECK IF SCRAP TOOL PRESENT AT TCU
           IF diScrapToolContact == FALSE THEN
              GetScrapTool()
           ENDIF
  • kwakisaki June 14, 2023 at 12:10 AM
    Approved the thread.
  • Hes
    42
    243
    • June 14, 2023 at 12:39 AM
    code is incomplete.. one case and no end switch. Move the variable declaration to dat file or make another that you can monitor. And check what the variable is when reaching the switch. Most likely error is as message states, value invalid.
  • hermann
    407
    2,612
    • June 14, 2023 at 6:13 AM
    And you must show the call of the program 'Toolchange', think you call it without a parameter. Should be something like Toolchange(#getscraptool)
  • Darkhorse
    17
    • June 14, 2023 at 12:25 PM
    Quote from Hes
    Thanks for reply. The code is pretty long that's why shared only one case, I do have multiple cases and also endswitch at the end. I can declare a new variable in dat file, but how do I use it within the switch logic to debug? If you could send a sample code, would appreciate it.
    panic mode
    1,280
    13,085
    • June 14, 2023 at 2:27 PM
    the part of code shown looks ok. parameter is declared correctly and it looks like it is not initialized. that means call was incorrect. you need to provide parameter value. this can be done either by creating test program that calls it, or... one can also enter parameter value from menu (if manually calling the routine). finally, one can also use VARSTATE function to check if the variable is initialized.
    for example add something like this:
    IF VARSTATE("eWorkToolSwitch")<>#INITIALIZED THEN
       IF $MODE_OP==#T1 THEN
          ; display dialog and ask user to select state manually
       ELSE
         MsgNotify("eWorkToolSwitch has no value")
         RETURN
       ENDIF
    ENDIF
  • Darkhorse
    17
    • June 15, 2023 at 12:30 PM
    Thanks guys. Seems like initialization was the issue as you guys mentioned. PLC is responsible for sending the initialization values as you can see on this line.
  • KSS 8.3