Multipass welding in Yaskawa YRC100
  • KUMAR UJJWAL
  • May 22, 2023 at 10:06 AM
  • KUMAR UJJWAL
    Hello folks,
    I am new to robot programming. I am trying to do multipass welding for which I have made a 'Job1' single-pass programme and I am calling Job1 in a For loop in another Job. However,after every pass, there should be an offset in Z-axis for the next pass. How do I do it? Is there an incremental mode option like the one we have in CNC, to set the last position of the robot as the new origin?
    Thank you.
  • Go to Best Answer
  • MOM May 22, 2023 at 10:17 AM
    Approved the thread.
  • TSGIR
    81
    714
    • May 22, 2023 at 8:39 PM
    For the multi pass in welding, there are a function in Yaskawa, that is multilayer.
    It need a hardware board and active some functions in the robot.
    You can use easy way too. Use shift instruction, SFTON instruction use for shift all Mov instructions in any direction that you need.
    For example:
    NOP
    SFTON P000 //set only z value ex. Z=20.000
    MOVL V=100
    MOVL V=100
    SFTOF
    END
    In this example all MOVL between SFTON and SFTOF will shift amount 20 mm in Z direction.
  • KUMAR UJJWAL
    • May 23, 2023 at 12:50 PM
    Thanks for the reply TSGIR .
    I tried your suggestion. I made two jobs, JOB1 and JOB2. JOB1 consists of the path with shift instruction at the end, as shown below:
    ---job1-----------it is the torch cycle (path)-----
    NOP
    MOVL V=50
    MOVL V=50
    MOVL V=50
    MOVL V=50
    SFTON P000
    END
    and I am calling job1 in job2 as shown below:
    ----job2------to repeate the torch path---
    NOP
    FOR I000 = 1 TO 5
    CALL JOB:JOB1
    NEXT I000
    END
    but, the problem is once the cycle is complet the shift happens only ones. I want the shift at the end of each cycle.
    Please advise.
  • TSGIR
    81
    714
    • May 23, 2023 at 1:29 PM
    • Best Answer
    You need to add the value of shift after each cycle to P000. Example you need each cycle the Z value increase 20 mm, the start job zero P000 , define other P001 position and only give Z value to it.
    After run each cycle in FOR, Add two position.
    ADD P000 P001
    At first cycle the shift value is 0
    At second cycle the shift value is 20 mm
    At 3rd cycle the shift value is 40 mm
    At 4rd cycle the shift value is 60 mm
    At 5rd cycle the shift value is 80 mm
  • KUMAR UJJWAL
    • May 23, 2023 at 4:32 PM
    It worked. Thanks a lot! TSGIR
  • Yaskawa YRC1000