    I am working with a R-30iA controller and an AB automaton
    Does anyone know how to write from an explicit message block (PLC) directly to a Register Position.
    I think it must be from the block configuration with instance, attribute and class.
    Under logix5000 I created a block with the different words x,y,z,w,p,r in DINT
    I could not find anything in the fanuc Ethernet Ip documentation
    Images
      • 16.1 kB
      • 590 × 381
      • 29
  • stare284
    24
    373
    • July 7, 2021 at 10:05 AM
    7.4.3 Position Register Object (0x7B, 0x7C, 0x7D, 0x7E)
    Located in the Ethernet/IP Setup and Operations Manual
  • automchamp
    17
    • July 7, 2021 at 11:48 AM
    Yes I had seen but there is only for the Joint mode
    By deduction I suppose that it is necessary to put this configuration but I am in error:
    For the POSREG_T, I used the same thing as on the doc for the chalkboard
  • HawkME
    567
    10
    3,268
    • July 7, 2021 at 7:48 PM
    Messaging position registers is only available on R-30ib or newer robots. (v8.1 or newer).
    You need to use regular numeric registers to send the x,y,z,w,p,r values individually to a different register then create a small TP program to set the PR element values to those numeric registers.
  • automchamp
    17
    • July 8, 2021 at 10:41 AM
    I have already done this task by sending values to 6 different registers and then assigning it to a PR with a TP program. But I think it is possible to write directly to a PR with explicit messaging. On page 128 of the Ethernet Ip manual, it shows the configuration for writing to a PR in Joint mode. On my side at source level I use a block like on page 119, but without success
    From what I understand in the manual.
  • HawkME
    567
    10
    3,268
    • July 8, 2021 at 1:09 PM
    In that manual it also says you need v8.1 or newer software. Can you check your version first?
    Honestly, I prefer the simpler register method. Why complicate it?
  • automchamp
    17
    • July 8, 2021 at 1:45 PM
    This is to simplify the program on the automation side as well as the robot side. So that afterwards you don't need the little program that does R to PR.
    Studio 5000 is in v30 and the robot in V8.3
  • HawkME
    567
    10
    3,268
    • July 8, 2021 at 3:43 PM
    Ok thanks for verifying you have v8.3.
    You need to use class 7b for cartesian, not 7c.
    Also, you have Attribute set to 7, which would indicate PR[7] is to be written.
    If changing the class does not fix it then you should review the 44 byte data structure to ensure it matches up exactly as documented.
Similar Threads
  • Variable to keep the error message
    • Fabian Munoz
    • June 19, 2020 at 5:28 PM
    • Fanuc Robot Forum
  • Position register and offset
    • automchamp
    • June 21, 2021 at 3:46 PM
    • Fanuc Robot Forum
  • Explicit Messaging between R30iB and OMRON PLC
    • Famous_Fella
    • March 12, 2020 at 10:24 AM
    • Fanuc Robot Forum
  • How to display the errors of a Fanuc robot on an HMI
    • VHS
    • July 17, 2020 at 4:24 PM
    • Fanuc Robot Forum
  • Yaskawa YRC1000 Ethernet/IP Explicit Messaging
    • BlackSea
    • November 15, 2019 at 5:30 PM
    • Yaskawa Motoman Robot Forum
  • Modify Position Point with IHM
    • mathias39
    • June 25, 2019 at 8:11 AM
    • Fanuc Robot Forum