Is there a parameter that stops the last bit from being a sign bit?
User input groups
Noob1982 -
March 22, 2019 at 1:29 AM -
you can use the function Roll left or right in the ladder on the group input .
directly, no. You can move the value of the input group to an M register and then shift the M register left or right and put the result in an output group.
I'll probably just get my input numbers from the register by grouping them in the ladder. I just can't get it to read right when all the bits are turned on. If I turn them all on in one group I should get 255 but instead I get -1.
Sounds like you have parity turned on. What controller are you using?
It's the YRC1000 controller. This is a new feature that allows you to set up your own custom I/O groups. So I can start with saying I want the group to start at input 1 and make it up to 32 bits long. Problem with it right now is I can't use the full group only up to the last bit. Like I said before if I look at all 8 in a group instead of getting 255 I get -1. I understand it's a sign bit for positive or negative but it's stupid to have it the way it is because I can't use it if I turn on that last bit. I've asked Motoman about it but I haven't got an answer yet. As of right now I've mapped them to a group of inputs that I'll never use do I can make the 9 bits long allowing me to use the full group of 8.
I had a chance to play with a YRC and the User group function. The robot I was on only had 8 inputs attached to it so I can only say what I saw and what I did.
First of all I set a user group to start at input one and end at input 8. I can see the same thing as Noob1982, when all the inputs are on the group value is -1. If I only turned on input 8 I got a value of -128. I next set the group to end at 7 and got the same result, if all the inputs in a group are on the value is -1 and if only the last input is on I get a value of -64. Don't know why but I will ask around and see what can be fixed.
The next test I did was to set the group to end one value higher than what I had, so the group started at 1 and ended at 9. This seemed to make it happy. I got 255 when all the bits are on just like I should.
Next week (time permitting) I will try to make two and then three small groups to see what happens.
To somewhat expanded on this and explain why Doc is seeing what he is seeing.
Using Doc's example of a 8-bit user group, we are used to I/O as being only positive, 2 to the 8 power, or 0 to 255. A user group can be negative or positive values. To relate this to an I variable, 2 to the 16 power has 65536 combinations. If it were unsigned the values could only go 0 to 65535. If it is signed, like an I variable, then the values are split even positive and negative, -32768 to 32767.
Using an User Group of 8 bits has 256 combinations. It is signed. So the acceptable values are -128 to 127. The most significant bit denotes a positive or negative value.
Back to Doc's example:
When all the switches are on, switch 8 is saying the value is negative. A negative value will show in two's complement. This equates to -1 in two's complement. With only switch 8 on, still saying the value is negative, the twos complement value is -128.
Decimal Value Binary Twos Complement
0 0000 0000
1 0000 0001
2 0000 0010
126 0111 1110
127 0111 1111
-128 1000 0000 1000 0000
-127 1000 0001 0111 1110
-2 1111 1110 0000 0010
-1 1111 1111 0000 0001To get the two's complement negative notation of a value, you write out the number in binary. You then invert the digits, and add one to the result.
That's a great explanation. Thanks very much for taking your time to post it.
My message above assumes no parity. It's a different ballgame with parity as another bit in the group becomes the parity bit and lessens the values the group can be.