Plc with roboguide
  • Moises
  • September 15, 2018 at 9:16 AM
  • Nxt2010
    • May 18, 2021 at 4:02 PM
    • #21
    I've talked to others who have successfully configured and connected Roboguide as an EIP scanner.
    Are there any background programs running on your PC that might be preventing the connection from going ONLINE? (Per my post above).
    I couldn't get my Roboguide Adapter connection ONLINE until I started closing out background programs in task manager, and it finally took.
  • jmd2777
    34
    193
    • May 18, 2021 at 5:59 PM
    • #22
    Thanks Nxt2010. I did try stopping some of the background programs and services. I'll give it another attempt though. Maybe I can create a virtual machine with a fresh install of Windows to eliminate the possibility of interference from another program or service.
  • pdl
    269
    1,530
    • May 18, 2021 at 6:13 PM
    • #23
    RoboGuide does not play well with virtual machines. If it did, no one would have to pay for their software licenses. Fanuc very rarely will give anything out for free.
  • jmd2777
    34
    193
    • May 20, 2021 at 7:12 PM
    • Best Answer
    • #24
    I was able to connect to a Turck IO Block using Ethernet/IP with the Roboguide robot as the Scanner. I followed the instructions mentioned previously in this thread. But at first it still would not work. I could ping the IO Block from the Roboguide robot but the connection would remain OFFLINE.
    Finally I recorded some packets using Wireshark. One of the packets had "Connection Failure (0x01)" and "Extended Status" Revision mismatch (0x0116)". Those error codes are in the Fanuc Ethernet/IP manual. I set the Major Revision and Minor Revision to 0 in the Ethernet/IP connection settings on the Roboguide robot and it worked!
    The weird part is that I am almost positive that the values I was using for Major and Minor Revision worked when we connected the IO Block to a real robot. I can't test it right now, but we recorded all the settings we used when we previously had it connected to a real robot.
    I recommend using Wireshark to anyone trying to connect Roboguide to an Ethernet/IP device.
  • ABuyck-AI
    • January 25, 2023 at 4:21 AM
    • #25
    Hello all. I've been playing around with roboguide connected to a physical compact logic PLC via Ethernet/IP since back in 2018. Hugely helpful for developing complete applications at home.
    Our company just recently got access to FT Logix Echo and I've spent most of the day experimenting with getting an Echo controller on my laptop to talk to Roboguide on that same laptop.
    After sorting out many IP address issues... I think they're "seeing each other"... but I'm still getting the following error message.
    Has anyone successfully configured Logix Echo to Roboguide?
  • Gabdav
    16
    • June 22, 2023 at 11:46 PM
    • #26
    Instructions from Fanuc if some one needs it.
    Also there is another common problem not cover in the Fanuc manual. You should disable/kill the service "FactoryTalk Linx Instance01 Service"
    Files
    EIP_in_ROBOGUIDE_V3.pdf 968.52 kB – 163 Downloads
  • MANIKANDAN_S
    MANIKANDAN S
    65
    • August 21, 2024 at 11:40 AM
    • #27
    Hi Gabdav,
    I have a question about the document you provided. I couldn’t find the Ethernet/IP Scanner (R540) (which includes an Adapter) in the search. Can I use the Ethernet/IP Scanner (R785) instead? Additionally, will this work with the Fanuc LR Mate 200iD/4S Robot with R30ib controller?
    Thanks!
  • pdl
    269
    1,530
    • August 21, 2024 at 11:05 PM
    • #28
    Yes, the scanner option supercedes the adapter option.
    I can't personally vouch as to weather the procedure will work with an R-30iB; it may need a few minor adjustments, but it should work in general.
  • Arturo_SF
    • November 27, 2024 at 6:28 PM
    • #29
    Quote from sibrdave