hi, EVERYBODY.
Is there step-by-step manual to connect PLC and IRC5comact using TIA Portal.?
i have tried many times. but there are some errors in TIA
plc S-1200 AND iRC5 COMPACT
mr_ruslan -
February 12, 2018 at 1:13 PM -
What kind of errors do you get in TIA? Setting up the PN connection should be quite straightforward.
Which kind of RW do you have? From 6.5.01 there is a new GSD necessary.
thank you for attention and answer.
I have solved some problems, i could connect PLC and IRC5 compact. now i try to transfer DI/DO from IRB5compact(XS12-xs15).
Have you got manual to transfer signals in right way? -
Hey Mr. Ruslan,
I do not have a manual for this. However you can just use the Inputs and output of the PLC. if you use at TIA side Q0.0 ( correct adres can be seen in device configuration), at the robot side this is unitmap "0"
hope this helps,
Jeroen
i am also working on the same project connecting IRC5 with S7-1215 dc/dc/dc.
if you respectable kindly share some info that how they are interfaced.
regards -
Standard IO for IRC5 compact is DSQC 652, 16 input/16 output discreet IO. For profinet you should have the option for the profinet fieldbus adapter card or anybus profinet adapter.
here is manual