Hopefully this won't appear twice! So I have 2 Arc Mate 120iBe robots and both have been converted to Handling Robots and each has a 30iA TP, neither of them have ethernet installed on them. My plan is to have both of them able to communicate via ethernet, and so my question is: what is the difference between Ethernet/IP Adapter and Ethernet/IP Scanner, do I need one of each or 2 of the same? I plan to communicate both robots with a Compactlogix 5370 L2 PLC, but I don't know which Ethernet/IP option I need. Thanks
Fanuc Question
bbishop108 -
January 11, 2018 at 8:40 PM -
If the PLC is the scanner all you need it Adapter for both robots
The Ethernet/IP scanner option is when the robot is the "master" and will communicate with remote Ethernet/IP devices "slaves". You will set up the EIP nodes in the robot. The Ethernet/IP adapter option is used when the robot will be a slave on an Ethernet/IP LAN. You would use the adapter option for both robots if the Compactlogix PLC is the Ethernet/IP master. Also, don't confuse the Ethernet/IP options with the Ethernet used in a regular network, they are different. Ethernet/IP is a fieldbus protocol.
You need EIP Adapter software option.
But if by mistake you get EIP Scanner, it doesn't matter, because that software option includes EIP Adapter. So you will get both.
You need EIP Adapter software option.But if by mistake you get EIP Scanner, it doesn't matter, because that software option includes EIP Adapter. So you will get both.
I wouldn't order the scanner option if you don't need it, it's $2750 for the PAC code. The adapter option is $1650.
Thanks everyone, yes I see now that the Adapter should be all I need for my application!!!