Moving a LR Mate 200iD with R30iB Controller
  • rich43
  • June 13, 2017 at 7:51 PM
  • rich43
    16
    Material handling robot is in a machine and there is a machine external E-stop that is preventing me from moving the arm. I understand I may be able to change the state of UI 1 *IMSTP from TRUE to FALSE to temporary allow me to move the robot with the teach pendent. Once the robot is clear, i can then change UI 1 back to True and correct the external E-Stop issue.
    Does anyone know how to do that?
  • stare284
    24
    373
    • June 13, 2017 at 7:59 PM
    Does the robot have an external estop fault? Or does the machine it is working with have the fault?
    This information is needed to give you a more detailed answer.
    But to clear the IMSTP fault just go to
    MENU--->SYSTEM---->CONFIG----ENABLE UI SIGNALS and set it to FALSE.
    Images
      • 68.29 kB
      • 626 × 439
      • 26
    Files
    UI.JPG_thumb 28.02 kB – 26 Downloads
    Edited once, last by stare284 (June 13, 2017 at 8:20 PM).
  • HawkME
    570
    3,269
    • June 14, 2017 at 12:38 AM
    If it is a hardwired external estop then no, you can't and shouldn't be able to defeat it in the program. Why can't you reset the Estop first, then move the robot?
  • rich43
    16
    • June 14, 2017 at 3:09 AM
    HawkME - It was an external e-stop that needed to be corrected; however, needed to get robot moved first. I would never run the robot in that condition; furthermore, the same thing could have been accomplished with a couple of jumpers at the robot external e-stop terminal blocks but did not want to do that.
    Stare284 - Thank you for your response. That is what I was looking for. A way of quickly getting the robot to clear any hazard and then deal with the other issues.
    Thank you for your response and have a great day.
  • HawkME
    570
    3,269
    • June 14, 2017 at 5:32 AM
    I get what you are saying. Were you actually able to jog the robot with no EES signals and no jumper?
    **Update, I just tried jogging a robot that had an External Estop condition. Disabling UOP did nothing, I had to jumper the wires or reset the E-stop in order to jog again. If you have found out some other way around this I would be curious to know, but it would very much surprise me if Fanuc allowed you to bypass a hardwired safety circuit by changing something in the software (with the exception of safety over Ethernet).
    Edited once, last by HawkME (June 14, 2017 at 4:26 PM).
  • stare284
    24
    373
    • June 14, 2017 at 6:04 PM
    I believe the machine had the Estop fault NOT the robot.
    I asked in my first post and did not get an answer but assuming since he was able to move the robot that the machine had the fault.
  • rich43
    16
    • June 14, 2017 at 10:07 PM
    Yes, your assumption is correct. It was the machine that generated the external E-stop fault and not the robot.
  • rich43
    16
    • June 14, 2017 at 10:28 PM
    Furthermore, not interested in temp disabling all the UI input signals, just UI 1 which is *IMSTP.