In the past we had a project with KRC 2 connected as Profinet device to a Siemens S7 315 PLC.
I know I had to swap the bytes in the Siemens Plc to receive the correct values.
Now we have a project with KRC4 and Siemens S7 1500 plc.
Will we have to swap the bytes again, or will this not be necessary because it is a S7 1500 PLC, or is there
a configuration option in the Kuka so that you don't have to swap the bytes anymore?
Byte swapping
-
Plc_User -
May 29, 2017 at 11:41 AM -
Thread is marked as Resolved.
-
-
In WorkVisual, there is an option to byte-swap multi-byte signal assignments in the IO-mapping tab.
-
and if that is not good enough, WoV also allows mapping I/O point by point (bit by bit). who knows maybe one day there will be product not using intel or motorola endianness
-
That'll happen after we get honest politicians, government budgets that make sense, and genetically engineer flying pigs.
-
sigh... if it was OR, flying pigs would be soon enough...
-
CRISPR will probably get us pigs-with-wings within a decade, just because some genegineer will be trying to make a point. But I figure actually making them fly will take several years longer (not to mention a decade's worth of argument of whether "gliding" like a flying squirrel qualifies for the Guiness record).