I have kuka KRC2-360 , windows is XP , KRC is 5.4.14
I need I/O for move robot , When turn on cabinet connect signal LED is off but Run and I/O Run signal LED are ON.
now don't see Input ,
please help me .
what can I do ? for solve problem .
how I do connect wago 750-306
-
km427 -
June 13, 2016 at 8:30 AM -
Thread is marked as Resolved.
-
-
Give image wago
-
I hasn't Image of WAGO .
How can I install WAGO ? I need software
How can I purvey WAGO software ?
-
-
Send IOSYS.INI and your DEVNET.INI
-
please send me download link for install Wago 750-306 .
-
-
Do I must need install WAGO software ?
-
no . write what you already did that? Top shoot weigh as it is connected.
-
Hi,
The attached manual should clear up most issues but here are a few pointers for what they are worth
1) the devnet.ini file set the baudware an Mac ID , this must match the dip switch settings on the wago 306
2) Use method 2 in the examples. At some point along the way method one stopped being supported. the driver is dn2drv.oThe number in front of the value is the Wago 306 Mac ID in a line like INB=13,0 13 = mac ID
When they refer to Form 1 or Form 2 they mean format or method
If it does not work right away just start off with 1 input block and 1 output block. Once you get it working then things will start to make sense
(panic mode - fixed formatting issue)
-
My Bad
It looks like I uploaded a prohibited document.
Mea culpa. -
Hi
Thank you for help me.
-
I'm trying to do this exact same thing and have set the baud and macid in the devnet.ini.
I think the addresses need setting but not sure where or how to do it?
-
any such info is very well guarded and only revealed to high priests and wizards... whatever you do, don't google 750-306 manuals or check old posts here. it may bring bad luck, drought or mummy curse.