Sir,
I have connected the analog input module in Controller R-J3iB.I am using the laser sensor. i am getting the 0-10v supply on multimeter but on teachpendant it is showing some different values (40 to 11) and response of changing in that values is also very slow.Please help me out.Thanks in advance
Analog input module
amolghule7 -
April 21, 2016 at 4:27 PM -
try the laser set to mA not Volts. you should get better results.
I am using the laser sensor that gives only the 0-10v Output
The input signal on pendant is not like voltage, but usually on count (0-4000) on full scale.
Other point, 0-10v is noise sensitive and i don't know the refresh rate of Analog input.
Check the way you have wired the input, I had this problem and it fixed once I made sure that the wiring and the configuration matched. Depending on your input setup the input module will expect either current or 0-10v. I believe that the difference is jumping 1 connection but it may be 2. The wiring diagram you need should be in the input module manual.