We have a R30iB running a M-20iA/20M robot. For no apparent reason the robot stopped while operating and whole system locked up, the pendant has a white screen. Rebooted but still comes up with a white screen. Anybody experienced this abnormally and found a fix. thanks Leonardo
Pendant White Screen Lockup
-
LapUSA -
March 11, 2016 at 7:08 PM -
Thread is marked as Resolved.
-
-
Try replacing the teach pendant cable.
-
Check CRS20 tp cable at the panelboard and also the JRS15 going from panelboard to main bd.
Sent from my SM-G900P using Tapatalk
-
Did replacing the TP solve this issue?
-
Try controlled start, then cold start
-
I currently have this issue of white screen on an R30IB and M-410iB 140H. The Fault light on the controller is red but not on the TP seems like a cable issue or boot issue. The TP sometimes boots to a white screen with words related to not being able to connect to webserver. Replacing the TP cable solved the issue for about 2 hours. Replacing the TEACH PENDANT had no effect.
Any thoughts?
-
Make sure the connectors on the E-Stop unit and Main Board are well seated.
Just to rule out the TP & cable, swap them as a pair from a working controller.
You might also want to try a Cold Start by holding the Fault Reset button while the powers up.
-
We did not have a replacement cable or T.P. We purchased both and had them driven same day from Nashville to Memphis. Tried the cable and it worked for a few hours. Did a controlled start and everything has worked fine since. Now I'm upset with myself. Did we just spend $8,000 when a controlled stop repaired the problem or was it the cable?
Either way we needed a backup cable and T.P.. My Plant Manager had just authorized this purchase when signs of a problem started. Thanks for the reply to Cold Start. I think that would of fixed the problem.
-
The result is you now have spare parts to troubleshoot with and potentially save more down time in the future. You've gained knowledge & experience and have a better understanding of shortcomings that can be reduced thru additional training. Plenty of positive here, I wouldn't be too upset.
-
Do a controlled start and then a cold start. It will resend the configuration to the teach.
Or... do the magic button trick -- push the three "service" button -- and reboot the we interface of TP.
Regards
M
-
Could someone explain the difference between controlled, cold, and hot start, and when to use any of these? Also, wouldn't a normal bootup be considered a controlled start perhaps?
Thanks,
-
Normal = Cold, resets I/O to off, clears program state.
Hot is set in system config, replaces cold start as the normal startup method if enabled. Faster startup, maintains last I/O and program state.
Controlled is selected in the cycle power option or by holding certain buttons during startup. Allows modifying certain system parameters and variables or configuring added hardware.
-