I'm facing a FUSE01 Panel Board/EMG BOARD Frequently Blown Problem for my R30iA Weld Robot Controller of Arcmate-120iC.
In this we automated 02 Robots by Auxilary axis.
within a span of 8days 02 times fuse blowned!
As per Remedy in the Alarm we've checked & Monitored everything.but no any abnormality found.
anyone help me out please.
Thanks in Advance!
FUSE01 Panel Board/EMG BOARD FREQUENTLY BLOWN PROBLEM
-
swapnil -
December 31, 2015 at 6:21 AM -
Thread is marked as Resolved.
-
-
I think this fuse blowns with a short in the TP cable. Did you check this?
-
I had the same problem with my robot. Despite TP cable change did not improve. Finally, I would go with the grounding problem. EMG Board FUSE now not problems..
-
Yes. we just replaced the TP Cable which was twisted & may be short while robot running. since this no problem yet....upto 15days
-
Yes. we just replaced the TP Cable which was twisted & may be short while robot running. since this no problem yet....upto 15days
Great, I've been surprised to see how many issues are influenced by the TP cable messing up. We've went through 6 in 3 months at one point. Issues were like blown fuses, robot turning off, not loading up, not jogging in T2 but runs in Auto.