Yes . but I have no idea where exactly connect
inverter to krc2
-
widelec -
October 9, 2015 at 8:59 PM -
Thread is marked as Resolved.
-
-
that drawing is only showing jumper plug wiring....
all you see there are safety INPUTS to KRC. you need more detailed drawing and taking a look at safety OUTPUTS on your X11. -
-
so you do have all info - page 12 is overview of safety outputs... (or according to acrobat, 16 out of 92)
-
Panic mode you are able to explain to me where and how is to be done? I'm curious what you have in mind.
-
Lower left corner of the page shows X11 circuit....
Last four X11 contacts are outputs Drives On (channel A is 11-12, channel B is 29-30).
You can see that internally those circuits are just dry contacts (fused too).
Those contacts close when drives are on.... -
Thank you
I'll be working today. -
If I understand correctly, the channels A and B should work as a contactor. If I let go by pin 29+ 27V, then after starting drives Ishould receive the voltage at the junction 30.
-
-
no reaction to the launch drives on channel A and B
-
gates closed?
-
no . but during testing I plugged the plug bridged
-
It turns out that this card does not support the outputs A and B.
-
There is still the possibility of some sort of security weigh?
-