[R-30iB] Karel - reading and converting a 32-bit value
  • bidzej
  • September 29, 2015 at 10:23 AM
  • bidzej
    23
    592
    I have a problem regarding a laser distance sensor connected to a robot over ProfiNet. I need to read the distance value and then make some calculations with it in Karel.
    The thing is that the sensor returns the distance as a 32-bit value and the robot only accepts 16-bit analog or group inputs. Any experience on converting a 32-bit value and then using it for calculations in a Karel program?
  • ESIELI
    10
    5
    275
    • September 29, 2015 at 10:31 PM
    Quote from bidzej
    Can you send it to a PLC then to the robot?
    or
    You can convert it from Profinet to Serial with a converter
    That's just some things I could think of real quick. I'm sure Fanuc has a better solution to cope with this.
  • trinket
    17
    • September 30, 2015 at 2:23 PM
    What kind is your 32-bit value, REAL or INTEGER?
  • Nation
    Typical Robot Error
    542
    1,924
    • September 30, 2015 at 2:27 PM
    If it is an integer, is it signed or unsigned?
  • trinket
    17
    • September 30, 2015 at 3:04 PM
    Quote from Nation
    You're right, of ccourse
  • Nation
    Typical Robot Error
    542
    1,924
    • September 30, 2015 at 10:30 PM
    Since you wrote about pulling in the 32 bit number on group inputs, I went ahead and assumed it was unsigned.
    I wrote some code for parsing in a 32 unsigned integer. Unfortunately you can only get half way up until the karel code I wrote errors out (final 32 bit number must be less than 2,147,483,647) , as there is no way that I know of to declare in karel an unsigned integer.
    The code assumes that there are 4 group inputs (11-14) each holding one byte of information. This is then pulled in and combined in the karel code. Group input 11 is the least significant byte, and 14 is the most.
    Here is the code:
    PROGRAM ROB_FORUM
    %NOLOCKGROUP
    VAR
    GROUP_I				:ARRAY[4] OF BYTE
    RETURN_VAL,RESULT,STATUS 	:INTEGER
    BEGIN
    	GET_PORT_VAL(18,11,RETURN_VAL,STATUS)
    	GROUP_I[1]=RETURN_VAL
    	GET_PORT_VAL(18,12,RETURN_VAL,STATUS)
    	GROUP_I[2]=RETURN_VAL
    	GET_PORT_VAL(18,13,RETURN_VAL,STATUS)
    	GROUP_I[3]=RETURN_VAL
    	GET_PORT_VAL(18,14,RETURN_VAL,STATUS)
    	GROUP_I[4]=RETURN_VAL
    	RESULT=GROUP_I[1]+GROUP_I[2]*256+GROUP_I[3]*65536+GROUP_I[4]*16777216
    END ROB_FORUM
    The constants in the result equation do the same thing as a lshift does in C (<<).
    Edited once, last by Nation (October 1, 2015 at 12:56 AM).
  • ESIELI
    10
    5
    275
    • October 1, 2015 at 3:23 PM
    Quote from Nation
    Here is the code:
    PROGRAM ROB_FORUM
    %NOLOCKGROUP
    VAR
    BEGIN
    END ROB_FORUM
    Nation, I see you're using port type as "18". Where do you get the numbers for each port type?
  • Nation
    Typical Robot Error
    542
    1,924
    • October 1, 2015 at 4:24 PM
    Quote from ESIELI
    From the KLIOTYPS.KL file. If you have roboguide installed, do a search of your disk and you will find it.
  • ESIELI
    10
    5
    275
    • October 1, 2015 at 6:22 PM
    Quote from Nation
    Roboguide?? I wish.. lol My company is too cheap.
  • Latoff
    16
    • February 19, 2020 at 5:34 PM
    Nation , but how would you do it vice versa in case you need to write XYZWPR value into the I/O (groups)?
  • Nation
    Typical Robot Error
    542
    1,924
    • February 19, 2020 at 6:55 PM
    • #11
    First, don't bump 5 year old threads. This would have been better as a new thread.
    Depends on the resolution you need. Since groups are INT based, I would just multiply the components of the position by 10 or 100, write to 6 groups, and then divide on the other side.
    Also, depends on your communication method. There are far better ways to get position data out of the robot than by group outputs.
  • Latoff
    16
    • February 19, 2020 at 7:18 PM
    • #12
    That is the deal i should keep it like that to allow later to be compatible with various comm. methods.
    Ok, still i need to get from REAL values integer. What is then the command for "Divide without remainder" or is the the way to parse the REAL values?
    If possible can you please mention the Karel commands for that
  • Latoff
    16
    • February 19, 2020 at 7:45 PM
    • #13
    Ok , at least the digits before comma i can extract via String parsing
    x : REAL (1025.395)
    CNV_REAL_STR(x,4,0,x_str)
    x_short=SUB_STR(x_str,2,3)
    SET_STR_REG(1,x_short,STATUS)
    CNV_STR_INT(x_short,result)
    result = 102 INTEGER