I need some advice. I am using an i30B controller and Im trying to configure my I/O. Im connected to a Turck BL20-GW-EN-IP I/O module. I have given it an IP address and configured the scanner. But it keeps telling me its offline. The robot cant see the I/O. But I can ping it from the robot, and I can ping it from a pc. I have even tried a new ethernet cable from the robot to the module. Any suggestions would be greatly appreciated.
Ethernet/IP Configuration
-
mcnealweld -
November 12, 2013 at 1:18 AM -
Thread is Resolved
-
-
The scanner must be correctly configured for the connection size and the adapter input/output/configuration assembly instances.
This information must be provided by the adapter device manufacturer. -
All of the instances are correct according to the manufacturer.
-
Im curious if there is a bug in this new software. Its material handler pro V8.20. This robot is a copy of a previous cell that we made. Everything is identical except the software version.
-
Stupid question, but did you start the scanner?
Also, are you sure the Turck is acting as an adapter?