WorkVisual project analysis
No safety interface has been configured for 0.
WorkVisual project analysis
No safety interface has been configured for 0.
Good afternoon, my friends! Please tell me why these messages appear when downloading a project via workvisual from kuka officelite?
Good afternoon, my friends! Please tell me why these messages appear when downloading a project via workvisual from kuka officelite?
on a real robot you would need to configure safety interface or you would not be able to move robot. this means adding one of four possible safety interfaces (must be one, not more not less). that could be parallel safety (X11 or X11+X13) or one of three fieldbus interfaces (FSoE, CipSafety or ProfiSafe).
since you are using OfficeLite, hardware is not really present so message about safety interface configuration can be ignored.
or since in officelite you cannot use fieldbus safety interfaces, just click on first choice and let WorkVisual complete the project. adding SION-SIB-STD would basically be adding X11 interface. this way message will no longer be shown
or since in officelite you cannot use fieldbus safety interfaces, just click on first choice and let WorkVisual complete the project. adding SION-SIB-STD would basically be adding X11 interface. this way message will no longer be shown
Thanck you