I want to connect the physical Emergency stop button from the operator's workplace with HMI panel.
Initially, I thought to connect UI[1] (IMSTP), UI[2](Hold), UI[3](SFSPD) through the HMI and use the EES1 EES11 EES2 EES21 signals from E-STOP BOARD (figure 1) to connect the button (At the moment, there are just electrical jumpers on the E-STOP BOARD)
But after some thought, I began to doubt - maybe it's worth connecting only UI[1] (IMSTP) to the E-STOP button from physical robot output module (), instead of sending it via tcp/ip.
Is it safe enough? In this case, EES is not used.
Which would be more correct, to use "IMSTP" or "EES" to connect HMI signal R30-iB?
-
Leviafun -
February 5, 2024 at 7:21 AM -
Thread is Unresolved
-
-
Hi,
Imstp, Hold, Sfspd and Enable are not safety rated Inputs so should not be used with the safty circuit or as safety.
EES should be wired if you don't have a safety bus.
-
Just use the designated safety inputs for external emergency stops on TBOP13?
-
Hi,
Imstp, Hold, Sfspd and Enable are not safety rated Inputs so should not be used with the safty circuit or as safety.
EES should be wired if you don't have a safety bus.
Thanks, the most confusing thing was that my paper manual says: "IMSTP - this signal determines an emergency stop controlled by the system".
As I understand it, these are different categories of ESTOP. -
hello
There are several ways to connect emergency stops. Do you want to cut off all outputs instantly ?
And do you have safety plc ?
-
Thanks, the most confusing thing was that my paper manual says: "IMSTP - this signal determines an emergency stop controlled by the system".
As I understand it, these are different categories of ESTOP.This has nothing to do with Emergency Stop.
From the R-30iB Plus manual:All things related to machine safety (not meaning "do not injure the mechanical unit", but "do not injure humans") needs to be safety rated.
The UOP-signals are only "normal" digital signals, not safety signals.
-
This has nothing to do with Emergency Stop.
From the R-30iB Plus manual:All things related to machine safety (not meaning "do not injure the mechanical unit", but "do not injure humans") needs to be safety rated.
The UOP-signals are only "normal" digital signals, not safety signals.
I've already figured it out, thanks guys.
It is a translation error in the localized manual