Hi everyone
any help about the external I/o , universal I/O and the specific I/O how do they work together and why we need to link external I/O to universal I/O sometimes
thank you for any help
Hi everyone
any help about the external I/o , universal I/O and the specific I/O how do they work together and why we need to link external I/O to universal I/O sometimes
thank you for any help
The external I/Os are between your device (same as sensor or relay) and robot controller. The address of each external I/Os show the devices connect to with address. The address for external inputs are 20xxx and for external outputs 30xxx. This addresses couldn't use in the robot JOB therefore you need some addresses that can use in JOB. For it use universal I/Os. The external I/Os connect to universal I/Os to use in robot JOB.
For example the #20030 connected to #10, it means if the #20030 turn ON from output the #10 turn ON, #10 is IN#(1) and you can use in robot JOB.
If you don't connect these signals, you can see only the status of input and couldn't use it in robot JOB.
I hope it can help you.
For more info see the install and wiring manual.
The external I/Os are between your device (same as sensor or relay) and robot controller. The address of each external I/Os show the devices connect to with address. The address for external inputs are 20xxx and for external outputs 30xxx. This addresses couldn't use in the robot JOB therefore you need some addresses that can use in JOB. For it use universal I/Os. The external I/Os connect to universal I/Os to use in robot JOB.
For example the #20030 connected to #10, it means if the #20030 turn ON from output the #10 turn ON, #10 is IN#(1) and you can use in robot JOB.
If you don't connect these signals, you can see only the status of input and couldn't use it in robot JOB.
I hope it can help you.
For more info see the install and wiring manual.
Hi tsgir
thank you for your response
what is the way to connect them withe each other
The external I/Os are between your device (same as sensor or relay) and robot controller. The address of each external I/Os show the devices connect to with address. The address for external inputs are 20xxx and for external outputs 30xxx. This addresses couldn't use in the robot JOB therefore you need some addresses that can use in JOB. For it use universal I/Os. The external I/Os connect to universal I/Os to use in robot JOB.
For example the #20030 connected to #10, it means if the #20030 turn ON from output the #10 turn ON, #10 is IN#(1) and you can use in robot JOB.
If you don't connect these signals, you can see only the status of input and couldn't use it in robot JOB.
I hope it can help you.
For more info see the install and wiring manual.
For more information about change in ladder, see the concurrent I/O manual.
It explain about each signals, how use ladder instructions.