Hi guys,
Controller: YRC1000
PLC: Siemens 1214C DC/DC/DC and 1515F-2 PN
GSD File: gsdml-v2.35-yaskawa-cifx-20220126.xml (it came on the Yaskawa stick)
I have this weird issue that when I power down my control cabinet and let the PLC power up again, the Yaskawa as a profinet devices is not accessible anymore, and I have to add it again to the configuration and then it works fine. I am having this issue on two separate PLCs. I have tried the 2.42. GSD file version as well, it does not work at all.
The message is pretty generic:
9 von 50; Ereignis-ID: 16# 02:39CB
Fehler: Ausfall eines IO-Device - IO-Device nicht gefunden
I have to mention that I am able to establish the connection, and can exchange signals. But, after powering down and coming the next day I have to do it all again.
I have never had this issue with a profinet device. Has anyone had a similiar experience?