Ethernet Comunication with Allen Bradley PLC
  • jcarlson
  • November 4, 2021 at 6:26 PM
  • jcarlson
    Im trying to set up communications between a R30iB and a L83 and the controller has both the scanner and adapter options available. I need to exchange ~10 floating point numbers (I can make them dints if that helps) to and from the robot and plc. Ive been digging through some manuals and forums and all ive found are ways to do digital IO with the adapter option. Does anyone know how to exchange numbers?
    Thanks.
  • Fabian Munoz
    134
    Articles
    1,517
    • November 4, 2021 at 7:18 PM
    Hi jcarlon
    Welcome to the robot forum
    Do a search under Explicit messaging
    If you have access to manuals, look
    Ehernet/ip setup and operations manual MAROU91EN2171E Rev C
    Retired but still helping
  • jmd2777
    34
    193
    • November 4, 2021 at 7:37 PM
    An alternative method is to use Group Inputs. GIs will do a binary to decimal conversion. However you are limited to 16 bit unsigned integers. For floating point values you can scale the value and store it in an integer in the PLC.
    On the robot you go to the Config menu for the Group Inputs. Map the GIs to the Ethernet/IP connection (Rack 89, Slot X). Set the START PT to the bit where the value begins. NUM PTS is 16 maximum.
    You can use BG logic to convert the GI value back to a floating point and store it in a register.
  • jcarlson
    • November 4, 2021 at 9:04 PM
    Thanks for the tip on explicit messages. Im going to see if I can work it out from the manual.
  • HawkME
    570
    3,270
    • November 5, 2021 at 5:12 AM
    For MSG instruction to a robot register you can use dint or real. The Registers are 32 bit and will adapt to either type.