In this cases I use a standart button connected to external input and declare it in reservation start program. In this case I have a 2 buttons for 2 stations, but You need to have and stop or Hold buttons and external Emergency stop button connected to machine safety board. If You not use a external PLC not need to set to REMOTE MODE - USE a PLAY MODE with reservation start.
External E-stop
-
Jeik Donald Pereira Silva -
October 22, 2021 at 12:54 AM -
Thread is Unresolved
-
-
What generation of controller? It’s on the MXT board or the IM/YE-250 board. Generally there is a sticker near the board describing the PIN numbers.
-
See on the Door, there are a sticker, it show the pinout of the board that "95devils" told you, some pins on this board are jumper, on the sticker find EXESP_1+, EXESP_1-, EXESP_2+, EXESP_2-. (In the DX and YRC controllers pin 5,6,7,8 are for this work)
You must disconnect the jumpers between this pins and connect your EMG keys.