Configuration Issues with DeviceNet and Beckhoff
  • Hello Guys,
    I'm running to kind of similar problem on this tread:
    I tried to use last conversation but still could not figure it out . i'm using the same setup and coupler, (KRC2 ed05 and Beckhoff BK5250 with 4 DI and 4 DO modules). i have 120 ohm resistors at both ends and using devicenet card channel 2 LPDN.
    so already make sure about connectivity and resistors.
    These are my INIT files :
    ****dnsc_2sl*****
    [MODULE_STARTUP]
    INACTIV= ; Example: 1,5,6
    CONTINUE_WITH_WARNING= ; Example: 8,25
    [SCANNERCFG]
    NET_EPR=75
    NET_ISD=5
    NET_BACKGROUND_POLL_RATE=1
    NET_TX_RETRY_COUNT=1
    [1]
    MAC_ID=11
    VENDOR_ID=0108
    PRODUCT_TYP=0012
    PRODUCT_CODE=5200
    POLL_RESPL=2
    POLL_CMDL=2
    ***dnsc_2co***
    [CONFIG]
    MAC_ID=0
    LOGFILE=log/dnsc2.log
    DEBUG=1
    BAUDRATE=500
    OPTIONS=0
    SCANLIST_COMMENT=1
    ****devnet***
    [KRC]
    DEBUG=1
    BAUDRATE=500
    LOGFILE=log/devnet.log
    [1]
    MACID=11
    *****IOSYS****
    [CONFIG]
    VERSION=2.00
    [DRIVERS]
    DIAGDRV=22,cp_DiagInit,diagdrv.o
    ;DNSC6=20,dnsc6Init,dnsc6drv.o
    ;DNSC5=19,dnsc5Init,dnsc5drv.o
    ;DNSC4=18,dnsc4Init,dnsc4drv.o
    ;DNSC3=17,dnsc3Init,dnsc3drv.o
    DNSC2=13, dnsc2Init, dnsc2drv.o
    [DIAGDRV]
    ;COMMENT=Configuration not required
    [RSI]
    [DNSC1]
    [DNSC2]
    INB2=11,0,x1
    OUTB2=11,0,x1
    [DNSC3]
    [DNSC4]
    [DNSC5]
    [DNSC6]
    [IOLINKING]
    [ERX]
    [END SECTION]
    in my devicenet tool shows the "device ID doesn't match "i don't know what that means but i cant figure out where can i find this information which i just copied from last thread?
    VENDOR_ID=0108
    PRODUCT_TYP=0012
    PRODUCT_CODE=5200
    Any help would be thoroughly appreciate.
  • Back up.
    First off, do you have an LPDN two-channel DN card in your KRC2, or are you trying to use the X801 DN socket on the MFC card?
    Second, do you have power on the DN cable's 24V and 0V lines?
    Third, what are the states of the indicator LEDs on the KRC2's DN port, and on the remote devices?
  • Solid green or blinking green?
    Also, "already have power on the channel"? What does this mean? There should only be one 24VDC power supply on the DN bus. The LPDN card in the KRC has to get its power from the DN cable, it does not draw power from the KRC's motherboard.
    The DEVNET.INI file is not relevant if you are using the LPDN card. DEVNET.INI only applies to the X805 on the MFC card.
    What are the contents of the DNSC2.LOG file?
    Both channels on the LPDN card appear to be occupied. But the light for one is red, the other is dark. So one is not running, the other has no power.
  • it's solid green and every 10 sec turn to red(right one)-green(left one) blinking.
    about power supply, i connected my power supply to 24+ and 0 .
  • ****dnsc2****
    30/ 7/20 : 21:23:37, DNch(2): >---------> Start LPDN-Scanner driver (channel 2)
    30/ 7/20 : 21:23:37, DNch(2): Debugging : enabled
    30/ 7/20 : 21:23:37, DNch(2): Serial : 9600 KBaud, 8*data,no parity, 1*stop, hardware
    30/ 7/20 : 21:23:37, DNch(2): Scanlist comments : enabled
    30/ 7/20 : 21:23:37, DNch(2): LPDN MAC_ID : 0
    30/ 7/20 : 21:23:37, DNch(2): Baudrate : 500 KBaud
    30/ 7/20 : 21:23:37, DNch(2): WatchDog : enabled
    30/ 7/20 : 21:23:37, DNch(2): PCI memory : 0x14A18000
    30/ 7/20 : 21:23:37, DNch(2): PCI IO : 0x4400
    30/ 7/20 : 21:23:38, DNch(2): SW-ver. drv/fw/PLX : 3.00B2/3.11/2
    30/ 7/20 : 21:23:38, DNch(2): HW-ver. serial/board : 2528/0
    30/ 7/20 : 21:23:38, DNch(2): No slaves in scanlist-file projected
    30/ 7/20 : 21:23:38, DNch(2): LPDN-Scanner state: running (channel 2)
    30/ 7/20 : 21:23:39, DNch(2): ERROR: [11]: No device
    30/ 7/20 : 21:23:40, DNch(2): ERROR: [11]: No device
    ****LPDN2***
    LPDN_Scanner : Log Date 30/ 7/20 : 19:40:14
    30/ 7/20 : 19:40:14, DNch(2): >---------> Start LPDN-Scanner driver (channel 2)
    30/ 7/20 : 19:40:14, DNch(2): Debugging : enabled
    30/ 7/20 : 19:40:14, DNch(2): Serial : 9600 KBaud, 8*data,no parity, 1*stop, hardware
    30/ 7/20 : 19:40:14, DNch(2): Scanlist comments : disabled
    30/ 7/20 : 19:40:14, DNch(2): LPDN MAC_ID : 1
    30/ 7/20 : 19:40:14, DNch(2): Baudrate : 125 KBaud
    30/ 7/20 : 19:40:14, DNch(2): WatchDog : enabled
    30/ 7/20 : 19:40:14, DNch(2): PCI memory : 0x14A18000
    30/ 7/20 : 19:40:14, DNch(2): PCI IO : 0x4400
    30/ 7/20 : 19:40:16, DNch(2): SW-ver. drv/fw/PLX : 3.00B2/3.11/2
    30/ 7/20 : 19:40:16, DNch(2): HW-ver. serial/board : 2528/0
    30/ 7/20 : 19:40:16, DNch(2): No slaves in scanlist-file projected
    30/ 7/20 : 19:40:16, DNch(2): LPDN-Scanner state: running (channel 2)
    30/ 7/20 : 19:40:17, DNch(2): FlushOutputs
  • ok,
    I got ESD file from Beckhoff technical team includes all required setup.
    but after i corrected my product ID, the error message change to " data size doesn't match" ??
    ****BK5250.eds***
    $ EDS
    [Device]
    VendCode = 108;
    VendName = "Beckhoff Automation";
    ProdType = 12;
    ProdTypeStr = "Communications Adapter";
    ProdCode = 5250;
    MajRev = 1;
    MinRev = 1;
    ProdName = "BK5250 V01.01";
    Catalog = "BK5250";
    [IO_Info]
    Default = 0X0001; $ Poll Connection is default
    PollInfo = 0X000F, 1, 1;
    StrobeInfo = 0X000F, 1, 1;
    COSInfo = 0X0007, 1, 1;
    CyclicInfo = 0X000B, 1, 1;
    $ Input Connections
    $ Assemblies
    Input1=
    0, $ 0 bytes length, see terminal configuration
    0, $ all bits are significant
    0x000F, $ Poll, BitStrobe, Change of State and Cyclic
    "A+D Inputs with Status byte", $ Name
    6, "20 04 24 6F 30 03", $ Assembly Inst. 111
    "Mapping, see EDS-File or Manual"; $ Help String
    $ Mapping Info:
    $ Byte 0 to (n-1) :Analog Inputs
    $ Byte n to (m-1) :Discrete Inputs
    $ Byte m :Vendor specific status byte
    $ bit0 = Internal bus error
    $ bit1 = Config error
    $ bit2 = reserved
    $ bit3 = reserved
    $ bit4 = reserved
    $ bit5 = reserved
    $ bit6 = Bus Sense Error
    $ bit7 = Fieldbus error / idle mode
    Input2=
    "Discrete Inputs with Status byte", $ Name
    6, "20 04 24 70 30 03", $ Assembly Inst. 112
    $ Mapping Info:
    $ Byte 0 to (n-1) :Discrete Inputs
    $ Byte n :Vendor specific status byte
    $ bit2 = reserved
    $ bit3 = reserved
    $ bit4 = reserved
    $ bit5 = reserved
    Input3=
    "Analog Inputs with Status byte", $ Name
    6, "20 04 24 71 30 03", $ Assembly Inst. 113
    $ Mapping Info:
    $ bit2 = reserved
    $ bit3 = reserved
    $ bit4 = reserved
    $ bit5 = reserved
    $ Output Connections
    $ Assemblies
    Output1=
    "Analog + Discrete Outputs", $ Name
    6, "20 04 24 65 30 03", $ Assembly Inst. 101
    $ Mapping Info:
    $ Byte 0 to (n-1) :Analog Outputs
    $ Byte n to m :Discrete Outputs
    Output2=
    "Discrete Outputs", $ Name
    6, "20 04 24 66 30 03", $ Assembly Inst. 102
    $ Mapping Info:
    $ Byte 0 to n :Discrete Outputs
    Output3=
    "Analog Outputs", $ Name
    6, "20 04 24 67 30 03", $ Assembly Inst. 103
    $ Mapping Info:
    $ Byte 0 to n :Analog Outputs
  • That means that your POLL_RESPL or POLL_CMDL values do not match the hardware. The fastest way to resolve this is to use the Telnet diagnostics (see the PDFs) to query MAC-ID 11 directly and ask it what it's IO Size is. It will respond with a number of bytes In and Out.
  • okay, i finally figure it out:
    POLL_RESPL=2
    POLL_CMDL=1
    i don't know why but it works with 1 DI and 1 DO module.