Hi everybody,
I want to know if there is a way to unlink the UOP mapping to PMC?
I don't want to use PMC.
The PMC is stop but control the UOP anyway.
Thanks.
Hi everybody,
I want to know if there is a way to unlink the UOP mapping to PMC?
I don't want to use PMC.
The PMC is stop but control the UOP anyway.
Thanks.
Maybe u need to delete UOP logic in Level 1 or 2 by FANUC ladder Ⅲ, and save, compile, export the memory file and upload to you robot in control start mode.
Delete the internal I/O mapping for the UOP signals under the I/O -> PMC menu. You might need to remove them from your ladder program as well.
It's a used robot and I don't have Fanuc Ladder III.
I'm trying to have a new core software without PMC options.
Thanks!