Hello guys,
is there some way how to send information about AUTO mode to the PLC?
In basic logic:
When is selected AUTO MODE -- DO = HIGH
When is selected T1,T2 MODE -- DO = LOW
Is it possible?
Thank you for the reply.
Hello guys,
is there some way how to send information about AUTO mode to the PLC?
In basic logic:
When is selected AUTO MODE -- DO = HIGH
When is selected T1,T2 MODE -- DO = LOW
Is it possible?
Thank you for the reply.
There are a couple ways to do this. In menu>System>Config you can set the DO to use for Auto, T1, and T2. Or you can use IO Interconnect in the IO menu, then use SI/SO signals.
Also, if you don't like those ways you could us BG Logic.
Thank you very much.
What do you do if you assigned DO's but it does not work. Fully mapped DO's not used elsewhere, but they do not change state. Also if assigned in the past, why does it not change to the new one now?
Just use the UO signal for TP enabled.
Contemplated this, however not a true positive in auto indicator. This also doe not answer the pre-assigned but no longer needed ones still holding there assignment.
Then use TP not enabled and command ready signals together.
For your other issue check and see if you have enough IO size set for the PLC connection.
Also make sure those points are not double mapped to a different IO type or used in Interconnect or Ref Pos.