Goodmorning guys!
I'm pretty new to Kawasaki and starting to learn a lot!
So...now I have this challenge:
I'm using a kawasaki FS06L with D71 Controller europe spec, to unload a pallet of coolers, and place these into multiple stations for coining, measuring and then placing it onto a leaktester line.
The unload of the pallet (including trays) is working with vision!
Now the goal I want to reach is that the robot checks on loosing the vacuum after it got vacuum, so after it picks up a cooler (vacuum sensor kicks in)
Now if it looses the vacuum before I shut down the gripper (it moves through multiples subroutines), I want it to hold, and initialize it's home program, so the operator can put it home position manually and remove the cooler, then continue.
Somehow it just doesn't accept an interrupt in my 4th PC program... how should I solve this?
Also I am a beginner and could use some help with debugging my programs, because it's a little unstable with multiple variables counting up and down for requesting different vision models etc.
And I'm a little worried with my 32 inputs and 32 outputs being used already, and on top of that I need so include multiple "Handshakes" with a PLC.
Sorry for my bad english, still learning everyday!
Thanks a lot in advance guys! The forum helped me out multiple times already!
Checking vacuum while moving through multiple subroutines (PC TASK?)
brordautomation -
March 29, 2016 at 9:33 AM -
There are several elements to your question......
But to address your initial question.If you are using the ON/ONI instruction, this is classed as a motion command and cannot be used in a PC Program.
QuoteSomehow it just doesn't accept an interrupt in my 4th PC program... how should I solve this?
- Is this the way you are intending to monitor for the vacuum?
- I ask, as it is more common to use the ON/ONI command specifically for this, in which case you have to place it in your main routine.
- ON/ONI starts monitoring and IGNORE stops monitoring.
- Take care using the CALL instruction with this, unless managed, the robot WILL return to the next instruction after the CALL.....and may result in unexpected motion.
- I usually use this with a GOTO instead to prevent that.From the sounds of it though, you want to just hold the process.....until the operator interacts and carry on.
But it depends on just when in the process it can lose the vacuum.....you would be carrying on with no part.
- Or are you intending the operator to check the gripper is working, place the cooler back in the gripper and then carry on?If the operator is a necessity for a stoppage....then simplest way is to just hold the process and let the operator decide the best course of action.
- Get them to check/reload the gripper and just carry on.
- I would be tempted to just use a ONI and CALL vac_fail routine, set an immediate flag and have it 'conditionally paused' inside an IF/END or DO/UNTIL in that subroutine until a. gripper outputs on, b.part detected, c. vac sensor ok d. confirmation by the operator has been received and reset the flag and RETURN and carry on.
- That way if someone just kept pressing cycle start, it would sit in the stoppage routine conditionally until all conditions metMany different ways to manage it, my opinion is always keep it simple as possible.......
Dear Kwakisaki! THANK YOU SO MUCH!
I just thought a pc program would be easy for monitoring in the background so I didn't have to make a mess with interrupts through my entire program but I guess it can't be any other way.
I'm currently busy with putting the ONI instructions into the subprograms where it picks up an object, and putting the ignores after my gripper is disabled (Thus: a ignore function at every drop point).
I want the operator to manually move robot (with check-go) into home-pos doing the following: The interrupt will call "lost_object" wherein it will "BRAKE" Then a message will be prompted to my first IFdisplay to inform the operator it lost the object, then set a variable to 1, call go_home, then let the operator remove the lost object from the robot cell, then I want to continue somewhere else in my main program after he pressed cycle start; and in my go_home program it will check that same variable which makes sure that it does the following:
lostobject = 0
MC HOLD
MC PRIME HOOFD,,44
Otherwise it wil continue from where it went into interrupts and go to the next drop point without any object which can result in unnecessary waste of time.
I'm understanding this is a possibility even when all my interrupts are located in different subroutines?
My main program contains a lot of CALL functions so I think this way it is the most "stable possibility"?
By the way, 2 things:
What exactly do you mean with the setting the flag? (want to learn haha )
And as soon as there is a chance that an object falls on the floor, it must be checked by other staff for deviations because of our high quality guarantee. So it's not the intention to let the operator place anything back in the gripper.
Anyway, Thank you a lot for replying! You inspire me with the knowledge!
Maybe if you're okay with it, we can keep contact using something more real-time than the forum?
Thanks in advance! -
PC Programs are natively for monitoring, background comms and non motion instructions and have low priority as they sit at the very end of the CPU clock cycle.
Main priority is given to motion planning which is where all your motion instructions are executed and therefore the Main program area or 'foreground task' is for this purpose to maximise efficiently.
Therefore the most efficient way of programming is to minimise non motion instructions by putting them in a PC Program.Unfortunately, when it comes to interrupting the motion planner, then this has to be given priority, so therefore ON/ONI is classed as a motion instruction and prevented from being used in a PC Program.........
When I said 'flag' sorry old habits.......internal signals or true and false markers which get set.
- So if you have individual programs for each part of the process....set a flag at the beginning and clear it at the end and maybe monitor for it to determine what the operator must do to restart after the interruption.
- but you seem to be doing this already with lostobject = 0.......not the only way to do it, you could use TRUE or FALSE, or even 0 and -1......If the operator is not to put anything back in the gripper, then that part of process has not been completed, so therefore I would assume, that needs repeating....so just prime that part of the process from the start of the routine again.
- By having your lost object routine to look for the 'lost object' flag in conjunction with a CASE statement to select the correct program based on process markers and MC PRIME xxxxx that way......excluding the step no......PRIME/MC PRIME will always prime from step 1 as a default without needing to enter a step no.
- In the process routine always check at the beginning if a 'lost object' marker is set and then lock in a conditional statement and IF Panel message to force the operator to go into Teach Mode, manually move the robot clear, then Check/Go which would include motion to home, when it gets home, look for the dedicated signal for home and THEN reset any lost object/process markers.
- So if the operator was to press cycle start.....nothing would happen...until recovered to home and home dedicated signal is set and flags reset.
- Therefore you will always be in the correct program, correct location to restart that part of the process.Using PRIME and a step no. in automatic is not something I would recommend unless the step no. is part of the process that does some conditional checking first, otherwise you could move the robot to ANY location, and the PRIME,,step no may drive the robot through something.
- However, I am not saying it's wrong, just something to consider perhaps......I prefer to share any knowledge I have via the forum as it may benefit others, but feel free to PM me, but I would recommend utilizing the forum as much as possible, as there are a lot of users who frequent it and many ideas and comments from several people aid to the learning experience, plus as you get more experience, you'll assist others too...
Can you tell us what kind of gripper are you using?
Hello all, I'm using a vacuum gripper, how to explain this? A sucker which moves down until it gets a vacuum!
I understand kwakisaki and I will use the forum as much as possible!
However, I have a really large program so I don't know if it's appropriate to post it...
I want to keep it simple but the disadvantage is: If I let the robot just continue after its motion stopped due to the interrupt when losing it's vacuum. It will proceed with the movement, thinking it's placing a cooler in the coining station, which requires PLC clearance etc. all and all it takes too much time because it's gonna be placed in 24/7 automotive production!
What if I let it jump into a lost_object subroutine with my interrupt an just make it hold, without the homing etc. then the operator removes the lost object from robot cell. then when it presses cycle start (EXT.Cycle start via PLC) it start all the way on top of my main program.
Would my lost_object program look like:
.PROGRAM lost_object()
BRAKE
aantalgepakt = aantalgepakt+1 ;this is to tell my vision system it skips the current cooler handling so it's starts looking for the next one)
currmodel = currmodel+1 ;ditto
IFPDISP 1
IFPWPRINT 1="LOST COOLER, GO TO HOME-POSITION, CHECK ROBOT CELL AND RESUME WITH CYCLE START"
lostobject = 1
TWAIT 5 (for displaying the message above, because in my home program it will immediately print something else!)
CALL go_home
.END
The cycle through my home program, which is okay, then cycle start.
Then on the end of my home program i made this:
if Lostobject= true call hoofd (which is dutch for main)
on the start of my main program i made:
IF lostobject = true then goto afterlost (So it moves to the label afterlost, which is located where I want to let the robot continue!
I hope this is gonna work! -
Hi guys!
It worked out!
But now i'm just curious what you guys think of my program... :$
If anyone is interested then I'm willing to share via PM!Cheers guys!
Excellent, I was just reading through, but difficult to visualize complete operation without 'hands on'.
- I am very specific, so I would also 'destruct' test it also to see if any bugs present.
- If any are found, you at least know that the 'core' programs are working.......and then resolve them etc.
- If it operates in the way you intended, then WELL DONE.....always nice to see the results of hard work.You can post your filesave, it is allowed, but takes long time to scroll through............full file save is not too large.....but takes long time to scroll through it.
- If I post code, I try and limit it to the main areas - maybe just program data.
- Check out variation of SAVE command switches (/p, /l, /r etc) in AS Manual - Section 5.3 I think......... -
What do you mean with destruct test?
I am testing at this moment and somehow it's doesn't listen to a Signalwat (SWAIT) instruction, it just continues without waiting for the signal. Checked my inputs, they're all off.
I will put my filesave (program data) beneath here (including my I/F panel so some of you can simulate it if you want):.INTER_PANEL_D
0,4,0,"TRAINING"," ON ON "," OFF OFF "," ",10,2,4,2219,2220,0
4,4,0,"VisionLink"," OFF OFF "," ON ON ","1 ",10,2,4,2251,2254,0
5,1," TCP Link"," "," 1"," ",10,15,4,0,2256,0
6,1," TCP Act."," "," 1"," ",10,15,1,0,2255,0
8,9,2,4,9
12,9,3,1,0
14,4,0," GRIPPER:"," VACUUM "," CLAMPING "," ",10,1,7,2202,2201,0
15,9,1,4,6
19,3," product"," search","","",10,4,13,0,0,2023,2024,0
20,3," product"," pick","set","",10,4,13,0,0,2025,2026,0
21,8,"invoernummer"," product"," number",10,11,3,1,0
22,8,"invoerhoogte"," product","height(mm)",8,12,3,2,0
23,8,"invoerhoek"," corner-"," rot.",9,12,5,2,0
24,8,"invoerkantelx","tilt"," tool x",9,12,5,2,0
25,8,"invoerkantely","tilt"," tool y",9,12,5,2,0
26,3," save","values"," in ","database",10,4,13,0,0,2027,2028,0
27,3," load","values"," from ","database",10,4,13,0,0,2021,2022,0
28,4,0,"production"," OFF OFF ON ON "," ON ON "," ",10,2,4,2219,2220,0
29,4,2,"VISIONLINK","OFF","ON","1",10,2,4,2251,2254,0
30,4,2,"Calibrated?NO","NO","YES","",10,2,4,0,2001,0
31,10,"LINEAIR","LEAVE","200MM","",10,4,6,0,"do ldepart 200",0
32,4,2,"VACUUM","ON","OFF","",10,4,2,11,0,0
35,8,"aantalgepakt"," caught","number",10,11,2,1,0
36,8,"watzoeken","Where","start?",10,11,2,1,0
37,8,"currmodel","currmodel","",10,11,2,1,0
38,10,"GO HOME","","","",10,4,6,1,"do jmove #thuis",0
42,8,"metkoeler","SPEED IN %","WITH COOLER",10,2,3,1,0
43,8,"mettray","SPEED IN %","WITH TRAY",10,9,3,1,0
44,8,"zonderobject","SPEED IN %","GENERAL",9,1,3,1,0
45,10,"ZERO POS","IN CASE OF","CONTROLLER","SHUTDOWN",10,2,6,2,"do jmove #zero",0
49,9,3,4,6
.END
.INTER_PANEL_COLOR_D
182,3,224,244,28,159,252,255,251,255,0,31,2,241,52,219,
.END
.SIG_COMMENT
.END
.PROGRAM al()
SPEED 100 ALWAYS
ALIGN
.END
.PROGRAM autostart.pc()
MC prime hoofd
CALL tcpcomm
.END
.PROGRAM autostart2.pc()
CALL pcif
.END
.PROGRAM autostart3.pc()
CALL pc3
.END
.PROGRAM cameracheck()
SPEED metkoeler ALWAYS
JAPPRO #voorcamera,200
ACCURACY 1
JMOVE #voorcamera
PULSE o_cam_start,1
DO
IF SIG(i_camera_goed) THEN
CALL fsp3
RETURN
END
IF SIG(i_camera_fout) THEN
CALL nio
RETURN
END
UNTIL FALSE
RETURN
.END
.PROGRAM database()
IFPDISP 1
IF invoernummer<>invoernummeroud THEN
invoernummeroud = invoernummer
nr = invoernummer
$nr = "["+$ENCODE(/I3,nr)+"]"
IF EXISTCHAR("$db_model"+$nr) THEN
IFPWPRINT 1="Model "+$nr+" selected: "+$db_model[nr]
ELSE
IFPWPRINT 1="Model "+$nr+" selected: vision name unkown yet"
END
END
IF SIG(s_loadfromdb) THEN
IF NOT SWITCH(TPKEY_S ) THEN
IFPWPRINT 1="Use the S key with this button to load values from the database"
SWAIT -s_loadfromdb
GOTO next1
END
nr = invoernummer
IF nr<1 OR nr>9999 THEN
IFPWPRINT 1="Non-valid PRODUCTNUMBER"
SWAIT -s_loadfromdb
GOTO next1
END
$nr = "["+$ENCODE(/I,nr)+"]"
IF NOT EXISTREAL("corr_rx"+$nr) THEN
corr_rx[nr] = 0
END
IF NOT EXISTCHAR("$db_model"+$nr) THEN
$db_model[nr] = "*"
END
IF NOT EXISTREAL("corr_ry"+$nr) THEN
corr_ry[nr] = 0
END
IF NOT EXISTREAL("corr_rz"+$nr) THEN
corr_rz[nr] = 0
END
IF NOT EXISTREAL("corr_z"+$nr) THEN
corr_z[nr] = 0
END
IF NOT EXISTREAL("db_grijper"+$nr) THEN
db_grijper[nr] = 0
END
invoerkantelx = corr_rx[nr]
invoerkantely = corr_ry[nr]
invoerhoogte = corr_z[nr]
invoerhoek = corr_rz[nr]
$lastfound = $db_model[nr]
IF db_grijper[nr]==0 THEN
SIGNAL s_vacuumgrijper,-s_klemgrijper
ELSE
SIGNAL -s_vacuumgrijper,s_klemgrijper
END
PULSE s_loadfromlamp,2
IFPWPRINT 1="Values loaded from database"
SWAIT -s_loadfromdb
END
IF SIG(s_savetodb) THEN
IFPWPRINT 1="Use the S button with this key to save values to database"
SWAIT -s_savetodb
GOTO next1
END
nr = invoernummer
IFPWPRINT 1="NON-VALID PRODUCTNUMBER"
SWAIT -s_savetodb
GOTO next1
END
corr_rx[nr] = invoerkantelx
corr_ry[nr] = invoerkantely
corr_z[nr] = invoerhoogte
corr_rz[nr] = invoerhoek
$db_model[nr] = $lastfound
IF SIG(s_vacuumgrijper) THEN
db_grijper[nr] = 0
ELSE
db_grijper[nr] = 1
END
PULSE s_savetolamp,2
IFPWPRINT 1="Values saved in database"
SWAIT -s_savetodb
END
IF SIG(s_trainingon) THEN
IF SIG(s_zoekknop,-s_zoeklamp) THEN
IF SIG(-2254) THEN
IFPWPRINT 1="Communication not active!"
SWAIT -s_zoekknop
GOTO next1
END
$gezochtmodel = $vismodellen[nr]
SIGNAL s_zoeklamp
maxmodel = 1
modelcount = 0
SWAIT -s_zoekknop
TIMER (2) = 0
SIGNAL -2252,2253
IFPWPRINT 1="Search is activated"
END
IF SIG(s_zoeklamp,2252,-2253) THEN
IF modelcount>0 THEN
$iftxt1 = "Model "+$vismodellen[0]+" found: "
$iftxt2 = "X: "+$ENCODE(/F6.1,visxvals[0])+"mm, Y: "+$ENCODE(/F6.1,visyvals[0])+"mm, ROT.: "+$ENCODE(/F5.1,vishoeken[0])+" deg."
$iftxt3 = "Searchtime: "+$ENCODE(/I5,TIMER(2)*1000)+"ms"
IFPWPRINT 1=$iftxt1,$iftxt2,$iftxt3
testx = visxvals[0]
testy = visyvals[0]
testhoek = vishoeken[0]
$lastfound = $vismodellen[0]
ELSE
IFPWPRINT 1="model not found"
END
SIGNAL -s_zoeklamp
END
END
RETURN
next1:
TWAIT 2
IFPWPRINT 1=""
.END
.PROGRAM fsp3()
SWAIT (i_wt_aanwezig)
JAPPRO fsp3,500
ACCURACY 1 ALWAYS
LAPPRO fsp3,100
SPEED 50 MM/S
LMOVE fsp3
SIGNAL -o_zuiger
IGNORE 1013
IF SIG(i_prog2) OR (i_prog3) THEN ;Same as in the program inpraegen because it needs to count to know where it's at.
END
SPEED zonderobject ALWAYS
ACCURACY 500 ALWAYS
TWAIT 0.2
LDEPART 500
PULSE o_fsp3,1
JMOVE #thuis
RETURN
.END
.PROGRAM go_home()
IFPDISP 1
check:
IF SIG(-s_home) THEN
IFPWPRINT 1,1,1,1,6="Robot isn\'t in home position. Jog robot to homeposition in TEACH mode with CHECK-GO"
SWAIT s_teach
SPEED 20
cond = 0
JMOVE #thuis
SIGNAL -o_zuiger
WHILE cond==0 DO
IF SIG(-s_teach) THEN
BRAKE
GOTO check
END
IF SIG(s_home) THEN
IFPWPRINT 1,1,1,1,6="Robot reached homeposition. The program can now be started with repeat."
cond = 1
IF lostobject==TRUE THEN
RETURN
END
END
END
END
IF SIG(-s_home) GOTO check
.END
.PROGRAM hoofd()
GOTO afterlost IF lostobject==TRUE
IFPDISP 2
;****** Main Program ******
;****** During startup: IO will be initialized ******
;****** Go to Home position in teach with check-go ******
;****** if not in home yet,then it starts ******
;****** a program depending on PLC signal and ******
;****** executes this. When looking for coolers:******
;****** order is: traycoordinates>pick 4 coolers ******
;****** >put tray away. ******
CALL rfa
CALL iolijst
; INIT SPEED & ACCURACY
ACCURACY 500 ALWAYS
CALL go_home
; ******* Initialisatie Vision camera 1 ******
SIGNAL -2254,2251
TWAIT 1
SIGNAL 2254,-2251
IF SIG(-s_gekalibreerd) THEN
CALL viscalib
PAUSE
END
; ************ Main Program *************
begincheck:
IF NOT (EXISTREAL("corr_rx"+$nr) AND EXISTREAL("corr_ry"+$nr) AND EXISTREAL("corr_rz"+$nr) AND EXISTREAL("corr_z"+$nr) AND EXISTREAL("db_grijper"+$nr) AND EXISTCHAR("$db_model"+$nr)) THEN
IFPWPRINT 3="Model "+$nr+" isn\'t trained yet"
IFPDISP 1
PAUSE
GOTO begincheck
ELSE
IFPDISP 2
IFPWPRINT 3="Model "+$nr+" is active"
END
SIGNAL (o_readynaarplc) ;Output 21, io initialized, calibrated, program set.
PAUSE ; Wait for EXT.cycle start from PLC!
WHILE TRUE DO
afterlost: lostobject = FALSE
; **** program according to PLC HMI choices *******
programma1:;program 1
IF SIG(i_prog1) THEN
IF SIG(i_metengoed) THEN
CALL uitmeten
CALL fsp3
END
IF SIG(i_metenfout) THEN
CALL uitmeten
CALL nio
END
IF SIG(i_praegengoed) THEN
CALL uitpraegen
CALL inmeten
END
IF SIG(i_praegenfout) THEN
CALL uitpraegen
CALL nio
END
IF TRUE THEN ;SIG(i_palletinpos,-i_palletleeg) THEN
CASE aantalgepakt OF
VALUE 4,9,14,19: ;decides if it needs to pick up a tray after it took 4 objects etc.
JMOVE #thuis
CALL paktray
JMOVE #viapos
CALL trayweg
IF aantalgepakt==20 THEN
aantalgepakt = 0
watzoeken = 1
JMOVE #thuis
SWAIT (i_palletinpos)
END
GOTO programma1
VALUE 0,5,10,15: ;Decides if it needs to start a new search command.(4 stacks)
JMOVE #thuis
SIGNAL s_zoek1,-s_gevonden1
CALL pak
JMOVE #viapos
CALL inpraegen
GOTO programma1
VALUE 1,2,3,6,7,8,11,12,13,16,17,18:
JMOVE #thuis
CALL pak
JMOVE #viapos
CALL inpraegen
GOTO programma1
END
ELSE
IFPWPRINT 3="Pallet isn\'t in position or empty"
JMOVE #thuis
PAUSE
GOTO programma1
END
IF watzoeken>=8 THEN
watzoeken = 1
GOTO programma1
END
END
programma2:;program 2
IF SIG(i_prog2) THEN
JMOVE #thuis
CALL paktray
JMOVE #viapos
CALL trayweg
aantalgepakt = 0
watzoeken = 1
JMOVE #thuis
END
GOTO programma2
JMOVE #thuis
CALL pak
JMOVE #viapos
CALL fsp3
GOTO programma2
JMOVE #thuis
CALL pak
JMOVE #viapos
CALL fsp3
GOTO programma2
END
ELSE
JMOVE #thuis
PAUSE
GOTO programma2
END
watzoeken = 1
GOTO programma2
END
END
programma3:
IF TRUE THEN ; NORMALLY: IF SIG(i_prog3) THEN
JMOVE #thuis
CALL paktray
JMOVE #viapos
CALL trayweg
aantalgepakt = 0
watzoeken = 1
JMOVE #thuis
END
GOTO programma3
JMOVE #thuis
CALL pak
JMOVE #viapos
CALL cameracheck
GOTO programma3
JMOVE #thuis
CALL pak
JMOVE #viapos
CALL cameracheck
GOTO programma3
END
ELSE
JMOVE #thuis
PAUSE
GOTO programma3
END
watzoeken = 1
GOTO programma3
END
END
END ; end of while
.END
.PROGRAM inmeten()
SWAIT (-i_metenbezet) ;wait for empty measuring station.
SPEED metkoeler ALWAYS ;speed with cooler
JAPPRO meten,500
ACCURACY 1 ALWAYS
LAPPRO meten,100
SPEED 50 MM/S
LMOVE meten
SIGNAL -o_zuiger
IGNORE 1013
TWAIT 0.2
LDEPART 200
PULSE o_meten,1
ACCURACY 500 ALWAYS
JMOVE #thuis
RETURN
.END
.PROGRAM inpraegen()
RETURN
END
SWAIT (-i_praegenbezet) ;wait for empty coining station.
JAPPRO praegen,500
ACCURACY 1 ALWAYS
LAPPRO praegen,100
SPEED 50 MM/S
LMOVE praegen
SIGNAL -o_zuiger
IGNORE 1013
TWAIT 0.2
LDEPART 200
PULSE o_praegen,1
ACCURACY 500 ALWAYS
JMOVE #thuis
RETURN
.END
.PROGRAM iolijst()
; Outputs (1 to 4 are a 1 second pulse to PLC).
o_afkeurband = 1 ;Robot gives this signal when he put the cooler on the belt and is out of area.
o_praegen = 2 ;Robot gives this signal saying that coining station is cleared to start.
o_meten = 3 ;Robot gives this signal saying that measuring station is cleared to start.
o_fsp3 = 4 ;Robot gives this signal saying that leaktesting tray is cleared to start transport cooler (out of area).
o_cam_start = 5 ;Start camera check.
o_grijperdicht = 9 ;Toggles double solenoid for clamping tool (optional).
o_grijperopen = 10 ;ditto.
o_zuiger = 11 ;toggles vacuumvalve.
o_readynaarplc = 21 ;Robot tells PLC that IO-list is initialized and ready for cycle start.
; DEDICATED OUTPUT SIGNALS
; TEMPORARILY : 17 = ROBOT IN AUTOMATIC.
; 22 = DEDICATED HOME SIGNAL..
; 29 = CYCLE START
; 30 = ROBOT IN AUTOMATIC (NOW TEMPORARILY 17).
; 31 = ERROR.
; 32 = MOTOR POWER ON!.
; DEDICATED INPUTS SIGNALS.
;1030 = EXT.CYCLE.START.
;1031 = EXT.ERROR.RESET.
;1032 = EXT.MOTOR.ON.
; Inputs (From PLC to robot)
;Coining
i_praegenbezet = 1001 ;PLC Tells robot coining station is occupied.
i_praegenfout = 1003 ;PLC tells robot coining failed so it places cooler on NIO belt. (rejected cooler)
i_praegengoed = 1017 ;PLC tells robot coining succeeded so it continues with placing it into measuring station.
; Measuring
i_metenbezet = 1002 ;PLC tells robot measuring statio is occupied.
i_metenfout = 1004 ;PLC tells robot measuring failed so it places cooler on NIO belt. (rejected cooler)
i_metengoed = 1018 ;PLC tells robot measuring succeeded so it continues with placing it into FSP3 leaktesting station.
; NIO
i_nioband_vol = 1019 ;NIO belt is full, Robot waits until it's cleared again.
;Traystacks
i_traystacks_vo = 1020 ;Traystacks are full, robot waits until it's cleared by operator.
; FSP3
i_wt_aanwezig = 1005 ;PLC tells robot that FSP3 offers an empty tray (on which the robot waits when measuring is finished) and directly places cooler onto leaktesting tray when receiving this signal.
;Camera
i_camera_goed = 1006 ;PLC tells robot that the camera approved the cooler so it places the cooler onto FSP3 leaktesting tray when above signal is received!
i_camera_fout = 1007 ;PLC tells robot that the camera rejected the cooler so it places the cooler onto NIO belt. (Cooler rejected)
;Pallet
i_palletinpos = 1008 ;As long as the pallet is in position the program 1,2 or 3 will cycle. After 1 cycle of 16 coolers robot waits until it receives this signal from PLC.
i_palletleeg = 1009 ;PLC tells robot that pallet is empty, Robot goes to home-position so the operator can reload the pallet station.
;Program mode from PLC ;after selection on HMI > EXT.CYCLE START from PLC.
i_prog1 = 1010 ;pick, coining, measuring, FSP3.
i_prog2 = 1011 ;pick, FSP3.
i_prog3 = 1012 ;pick, cameracheck, FSP3.
i_vacuum = 1013 ; &14,15,16 Occupied internally, not adjustable according to RFA mechanic.
s_zoek1 = 2006
s_zoekenactief1 = 2007
s_gevonden1 = 2008
; DON'T ADJUST BECAUSE IT'S RELATED TO I/F Panel!
s_trainingon = 2219
s_trainingoff = 2220
s_loadfromdb = 2021
s_loadfromlamp = 2022
s_savetodb = 2027
s_savetolamp = 2028
s_zoekknop = 2023
s_zoeklamp = 2024
s_pakkenknop = 2025
s_pakkenlamp = 2026
s_klemgrijper = 2201 ; gripperselection
s_vacuumgrijper = 2202 ; gripperselection
s_home = 22
s_home2 = 2011
s_teach = 2012
aantalgepakt = 0 ;vacuumcounter
watzoeken = 1 ;Selects wanted vision model (4 areas, 8 images: 1,3,5,7 = TRAY DETECTION. 2,4,6,8 = COOLER DETECTION)
basisz = -80 ;This needs to be changed when robot is mounted on floor!
lastdrop = 0 ;Keeping track of in which traystack it dropped the tray for the last time.
lostobject = FALSE ;Lost object?
currmodel = 0 ;Current cooler picknumber for coordinates arrayindex (point oppakpunt [] )
metkoeler = 30 ; Speed for moving with cooler in percentage of total speed!
mettray = 50 ; DITTO; speed with tray
zonderobject = 100 ;Speed without cooler
; SIGNAL (-s_gekalibreerd) ;activate this line if you want to enable calibration everytime IO-list is getting initialized.
.END
BRAKE
IFPDISP 1
lostobject = TRUE
TWAIT 5
CALL go_home
IFPWPRINT 3="PRIME hoofdprogramma"
IFPDISP 2
PAUSE
.END
.PROGRAM nio()
SWAIT (-i_nioband_vol)
JMOVE #bovennio
ACCURACY 1
JMOVE #dropnio
SIGNAL -o_zuiger
IGNORE 1013
TWAIT 0.2
PULSE o_afkeurband,1
LDEPART 500
JMOVE #thuis
RETURN
.END
.PROGRAM pak()
IF SIG(i_prog1) THEN ;DON'T pick up cooler when coining station is occupied (Program mode 1)
SWAIT (i_praegenbezet)
END
begin:
IF db_grijper[prnum]==0 THEN
currgrip = 0
o_grijper1 = 11
o_grijper2 = -11
i_grijper = i_vacuum
ELSE
o_grijper1 = 10
o_grijper2 = 9
currgrip = 1
i_grijper = 10 ; dummy, grijper dicht output gebruiken omdat er geen input is
END
TOOL toolnr[currgrip]
SIGNAL -o_grijper1,o_grijper2
JMOVE #thuis
VALUE 0,5,10,15:
SWAIT s_gevonden1
END
JMOVE #bovenpakken[currgrip]
lastgrip = currgrip
IF currmodel==3 THEN
POINT oppakpunt = TRANS(visxvals[3],visyvals[3],basisz+corr_z[prnum],corr_rz[prnum]-vis1hoek,180,0)+RX(corr_rx[prnum])+RY(corr_ry[prnum])
watzoeken = watzoeken+1
END
IF currmodel<3 THEN ;kan dit?
POINT oppakpunt = TRANS(visxvals[currmodel],visyvals[currmodel],basisz+corr_z[prnum],corr_rz[prnum]-vis1hoek,180,0)+RX(corr_rx[prnum])+RY(corr_ry[prnum])
END
IF INRANGE(oppakpunt) OR INRANGE(oppakpunt+TRANS(0,0,-100)) THEN
IFPWPRINT 3="Out of range"
GOTO begin
END
ACCURACY 1 ALWAYS
JAPPRO oppakpunt,100
SIGNAL o_zuiger
SPEED 50 MM/S
XMOVE oppakpunt+TRANS(,,50) TILL i_vacuum
ONI -1013 CALL lost_object
LDEPART 250
ACCURACY 500 ALWAYS
RETURN
.END
.PROGRAM paktray()
currmodel = 0
begin:
currgrip = 0
o_grijper1 = 11
o_grijper2 = -11
ELSE
o_grijper1 = 10
o_grijper2 = 9
currgrip = 1
END
JMOVE #thuis
SWAIT s_gevonden1
lastgrip = currgrip
POINT oppakpunt = TRANS(vis1xtray,vis1ytray,basisz+corr_z[prnum],corr_rz[prnum]-vis1hoektray,180,0)+RX(corr_rx[prnum])+RY(corr_ry[prnum])
GOTO begin
END
ACCURACY 1 ALWAYS
SIGNAL o_zuiger
SPEED 50 MM/S
SPEED mettray ALWAYS
LDEPART 250
ACCURACY 500 ALWAYS
RETURN
.END
.PROGRAM pc3()
1 IF SIG(s_trainingon) THEN
CALL database
END
IF SIG(s_trainingoff) THEN
CALL pcpallet
END
GOTO 1
.END
.PROGRAM pcif()
WHILE TRUE DO
IF BITS(s_trainingon,2)<>trainbitsoud THEN
IF WHICHTASK("hoofd")<0 THEN
MC zpow off
TWAIT 0.5
MC prime HOOFD
MC zpow on
IFPDISP 2
END
ELSE
IF WHICHTASK("testen")<0 THEN
MC zpow off
TWAIT 0.5
MC prime testen
MC zpow on
IFPDISP 1
END
END
trainbitsoud = BITS(s_trainingon,2)
END
END
.END
.PROGRAM pcpallet()
startzoek: IF SIG(s_zoek1) THEN
skipzoek:
SIGNAL -s_zoek1,s_zoekenactief1
modelcount = 0
maxmodel = 4
CASE watzoeken OF
VALUE 1: ;Tray linksboven
$gezochtmodel = $db_model[5]
prnum = 5
VALUE 2: ;Koelers linksboven
$gezochtmodel = $db_model[1]
prnum = 1
VALUE 3: ;Tray rechtsboven
$gezochtmodel = $db_model[6]
prnum = 6
VALUE 4: ;Koelers rechtsboven
$gezochtmodel = $db_model[2]
prnum = 2
VALUE 5: ;Tray linksonder
$gezochtmodel = $db_model[7]
prnum = 7
VALUE 6: ;Koelers linksonder
$gezochtmodel = $db_model[3]
prnum = 3
VALUE 7: ;Tray rechtsonder
$gezochtmodel = $db_model[8]
prnum = 8
VALUE 8: ;Koelers rechtsonder
$gezochtmodel = $db_model[4]
prnum = 4
VALUE 0,9,10:
IFPWPRINT 3="correct:\'Where start?\'"
TWAIT 5
GOTO skipzoek
END
SIGNAL -2252,2253 ; START VISION.
END
IF SIG(s_zoekenactief1,2252) THEN ; VISION COMPLETED
IF visstatus==6 THEN
IFPDISP 1
IFPWPRINT 2="wanted model isn\'t trained in vision!","train the model!"
SIGNAL -2254,2251
TWAIT 5
IFPDISP 2
GOTO skipzoek
ELSE
IFPWPRINT 2="Searching goes well"
END
IF (modelcount>0) THEN
IFPWPRINT 3="Objects found"
CASE watzoeken OF
VALUE 1,3,5,7:
vis1xtray = visxvals[0]
vis1ytray = visyvals[0]
vis1hoektray = vishoeken[0]
IF watzoeken==8 THEN
GOTO skipzoek
END
GOTO skipzoek
END
ELSE
IFPWPRINT 3="Not found-->Where am I > Where start?"
GOTO skipzoek
END
SIGNAL s_gevonden1,-s_zoekenactief1
END
GOTO startzoek
.END
.PROGRAM rfa()
IFPDISP 1
$text1 = " Robot is programmed by: "
$text2 = " Brord van der Linden. "
$text3 = " tel: 06-1173863? "
$text4 = " brordquad@gmail.comhttps://nl.linkedin.com/in/brord-van-der-linden-665177115 "
IFPWPRINT 1,1,1,4,2=$text1+$text2+$text3+$text4
TWAIT 5
IFPDISP 2
RETURN
.END
.PROGRAM tcpcomm()
; Hoofd communicatie programma voor Vision Link
; PARAMETERS:
; signal: 2256 - output status van de link
; signal: 2255 - output link activiteit
; signal: 2254 - link aan/uit
; signal: 2253 - data klaar om te versturen
; signal: 2252 - data ontvangen
; signal: 2251 - force vision uit (ism 2254)
; signal: 2250 - reserved
; signal: 2249 - reserved
; real: stat - reserved
; real: tcpretval - reserved
; real: tcpsockid - reserved
; real: tcpsendcount - reserved
; real: tcprecvcount - reserved
; string: $tcpsenddata[] - reserved
; string: $tcprecvdata[] - reserved
; real: ip[] - in: [1..4] De delen van het IP van de Vision PC (1.2.3.4)
; real: port - in: Het poort nummer waar de Vision software op draait
; real: visstatus - uit: status van laatste vis aanvraag
; real: modelcount
; in: start index model array
; out: aantal in model array (gerekend vanaf 0)
; real: maxmodel
; in: maximum aantal models
; uit: aantal opgehaalde models
; string: $gezochtmodel - in: model dat gezocht wordt (leeg = alles)
; string: $vismodellen[] - uit: array met modelnamen
; real: visxvals[] - uit: array met x waarden voor modellen
; real: visyvals[] - uit: array met y waarden voor modellen
; real: vishoeken[] - uit: array met hoeken van modellen
tcpsockid = -1 ; invalidate socket
SIGNAL -2255,-2256 ; reset lampen
tcpconnerrcnt = 0
init: IF (SIG(-2254)) THEN
CALL tcpcomm_close
END
SWAIT 2254
CALL tcpcomm_connect
IF tcpretval<0 THEN
; Error met TCP.. Retry maar
CALL tcpcomm_close; // voor de zekerheid
tcpconnerrcnt = tcpconnerrcnt+1
IF tcpconnerrcnt>9 THEN
; 10x fout
TYPE "Connectie met Vision kan niet gemaakt worden."
TYPE "Controleer of Vision draait en het netwerk goed is aangesloten."
tcpconnerrcnt = 0 ; reste voor volgende keer
SIGNAL -2254,2251 ; Force Vision uit
END
GOTO init
END
tcpconnerrcnt = 0 ; Connectie gemaakt, reset dus
; wacht op signal
wtrans: WAIT SIG(-2254) OR SIG(2253)
; wat hadden we?
skipwait: IF SIG(-2254) THEN ; TCP uit
CALL tcpcomm_close
GOTO init
END
IF SIG(2253) THEN ; Data te versturen
SIGNAL -2253
GOTO senddata
END
GOTO wtrans ; Signaal moet veranderd zijn...
senddata: $tcpsenddata[0] = "reqmodel|"+$gezochtmodel+"|"
$tcpsenddata[0] = $tcpsenddata[0]+$ENCODE(/I10,maxmodel)
tcpsendcount = 1
CALL tcpcomm_send
IF tcpretval<0 THEN
IF tcpretval==-1 OR tcpretval==-2212 OR tcpretval==-2232 THEN ; socket was dicht!
IF SIG(2254) THEN
IF tcpretval>=0 GOTO senddata ; Probeer nog een keer
CALL tcpcomm_close; voor de zekerheid
visstatus = 0
SIGNAL 2252
GOTO init
ELSE
visstatus = 0
SIGNAL 2252
GOTO init ; Ik was eigenlijk uit
END
ELSE
CALL tcpcomm_close
visstatus = 0
SIGNAL 2252
GOTO init ; reset comms maar
END
END
recvdata: CALL tcpcomm_recv
IF tcpretval<0 THEN
visstatus = 0
SIGNAL 2252
GOTO init ; Kan toch niet recoveren
END
; data binnen, bekijk
$temp = $DECODE($tcprecvdata[0],"|",0)
IF $temp=="notfound" THEN
$temp = $DECODE($tcprecvdata[0],"|",1) ; delete seperator
visstatus = VAL($temp)
SIGNAL 2252
GOTO wtrans
END
IF $temp=="found" THEN
temp = VAL($temp)
IF temp<maxmodel THEN
maxmodel = temp
END
IF maxmodel==0 THEN
maxmodel = temp
END
i = 1
count = 0
FOR count = 0 TO maxmodel-1
arrayindex = count+modelcount
IF (LEN($tcprecvdata[0])<120) AND (i<tcprecvcount) THEN
$tcprecvdata[0] = $tcprecvdata[0]+$tcprecvdata[i]
i = i+1
END
$vismodellen[arrayindex] = $temp
visxvals[arrayindex] = VAL($temp)
pno = arrayindex
visyvals[arrayindex] = VAL($temp)
vishoeken[arrayindex] = VAL($temp)
END
modelcount = modelcount+maxmodel
visstatus = 1
SIGNAL 2252
GOTO wtrans
END
; foutieve data
visstatus = 0
maxmodel = 0
SIGNAL 2252
GOTO wtrans
.END
.PROGRAM tcpcomm_close()
; Sluit een socket
; PARAMETERS:
; real: tcpsockid - ID van socket. Wordt ook naar -1 gezet
; RETURN VALUE:
; geen
IF tcpsockid<0 THEN
TYPE "Socked already closed"
RETURN
END
TCP_CLOSE stat,tcpsockid
SIGNAL -2256
tcpsockid = -1
TYPE "Socked closed"
.END
.PROGRAM tcpcomm_connect()
; connect naar de opgegeven Vision PC
; Protocol versie: 1
; PARAMETERS:
; real: port - poort nummer van server
; real[1..4]: ip - IP van server
; real: tcpsockid - ID van socket. Wordt naar socket id gezet bij succes
; RETURN VALUE:
; real: tcpretval - socket nummer, of negatief bij error
IF tcpsockid>=0 THEN
TYPE "Socket already connected"
CALL tcpcomm_close
tcpretval = tcpsockid
RETURN
END
TCP_CONNECT stat,port,ip[1]
IF stat<0 THEN
TYPE "Failed to connect to server"
tcpretval = stat
RETURN
END
tcpsockid = stat
; Connectie gemaakt, kijk of versies ed. kloppen
nr = 1
TCP_RECV stat,tcpsockid,$inarray[0],nr,10
IF stat<0 THEN
; iedere error is fout bij connecten
TYPE "Failed to receive welcome message"
tcpretval = stat
CALL tcpcomm_close
RETURN
END
$temp = $DECODE($inarray[0]," ",0)
IF $temp!="P1" THEN
TYPE "TCP protocol mismatch"
tcpretval = -1
CALL tcpcomm_close
RETURN
END
$temp = $DECODE($inarray[0]," ",1) ; Drop seperator
TYPE $inarray[0]
; Connectie gereed
SIGNAL 2256
RETURN
.END
.PROGRAM tcpcomm_recv()
; Ontvang data over de socket
; PARAMETERS:
; string: $tcprecvdata[] - ontvangst buffer, beginnend bij index 0
; real: tcprecvcount - aantal ontvangen strings
; RETURN VALUE:
; real: tcpretval - 0 als OK, sock error id bij error, -1 bij geen sock
IF tcpsockid<0 THEN
TYPE "Socket isn\'t open"
tcpretval = -1
RETURN
END
SIGNAL 2255
TCP_RECV stat,tcpsockid,$tcprecvdata[0],tcprecvcount,30,120
DLYSIG -2255,1
IF stat<0 THEN
tcpretval = stat
IF stat==-2212 THEN
TYPE "Socket was remotely closed"
CALL tcpcomm_close
RETURN
END
IF stat==-2232 THEN
TYPE "Socket locally closed without notice"
tcpsockid = -1
RETURN
END
RETURN
END
; Data is ontvangen
TYPE $tcprecvdata[0]
tcpretval = 0
RETURN
.END
.PROGRAM tcpcomm_send()
; Stuur data over de socket
; Verbreekt de verbinding als de socket remote gesloten is.
; PARAMETERS:
; string: $tcpsenddata[] - te versturen strings, beginnend bij index 0
; real: tcpsendcount - aantal te versturen strings
; RETURN VALUE:
; real: tcpretval - 0 als OK, sock error id by error, -1 bij geen sock
IF tcpsockid<0 THEN
tcpretval = -1
RETURN
END
SIGNAL 2255
TYPE $tcpsenddata[0]
TCP_SEND stat,tcpsockid,$tcpsenddata[0],tcpsendcount,15
;TYPE $tcpsenddata[0]
DLYSIG -2255,1
IF stat<0 THEN
tcpretval = stat
IF stat==-2209 THEN
TYPE "To much data for socket"
RETURN
END
IF stat==-2212 THEN
CALL tcpcomm_close
RETURN
END
IF stat==-2232 THEN
tcpsockid = -1
RETURN
END
END
; Data is verzonden
tcpretval = 0
RETURN
.END
.PROGRAM testclamps()
1 SIGNAL o_zuiger
SWAIT i_vacuum
TWAIT 2
SIGNAL -o_zuiger
IGNORE 1013
TWAIT 0.2
TWAIT 2
GOTO 1
.END
.PROGRAM testen()
lastgrip = -1
CALL testpakken
.END
.PROGRAM testpakken()
begin:
currgrip = 0
ELSE
currgrip = 1
END
IF currgrip<>lastgrip THEN
lastgrip = currgrip
END
POINT oppakpunt = TRANS(testx,testy,basisz+invoerhoogte,invoerhoek-testhoek,180,0)+RX(invoerkantelx)+RY(invoerkantely)
JMOVE SHIFT(oppakpunt BY 0,0,0)-TRANS(0,0,100)
LMOVE SHIFT(oppakpunt BY 0,0,0)
BREAK
LMOVE SHIFT(oppakpunt BY 0,0,0)-TRANS(0,0,100)
GOTO begin
.END
.PROGRAM testtool()
JMOVE #bovtest1
LMOVE SHIFT(testtool BY 0,0,30)
LMOVE SHIFT(testtool BY 0,0,0)
BREAK
JMOVE #bovtest1
JMOVE #bovtest2
LMOVE SHIFT(testtool BY 0,0,30)+RZ(180)
LMOVE SHIFT(testtool BY 0,0,0)+RZ(180)
BREAK
JMOVE #bovtest2
.END
.PROGRAM trayweg()
SWAIT (-i_traystacks_vo) ;Wait for empty traystack station.
ACCURACY 10 ALWAYS
IF lastdrop==1 THEN
JMOVE #bovendrop2
LMOVE #droptray2
SIGNAL -o_zuiger
IGNORE 1013
LMOVE #bovendrop2
lastdrop = 2
ELSE
JMOVE #bovendrop1
LMOVE #droptray1
SIGNAL -o_zuiger
IGNORE 1013
LMOVE #bovendrop1
lastdrop = 1
END
ACCURACY 500 ALWAYS
JMOVE #thuis
RETURN
.END
.PROGRAM uitmeten()
IF SIG(i_metenbezet) THEN
JAPPRO meten,500
ACCURACY 1 ALWAYS
LAPPRO meten,50
SIGNAL o_zuiger
SPEED 50 MM/S
XMOVE meten+TRANS(,,50) TILL i_vacuum
LDEPART 200
ACCURACY 500 ALWAYS
END
RETURN
.END
.PROGRAM uitpraegen()
IF SIG(i_praegenbezet) THEN
JAPPRO praegen,500
ACCURACY 1 ALWAYS
LAPPRO praegen,50
SIGNAL o_zuiger
SPEED 50 MM/S
XMOVE praegen+TRANS(,,50) TILL i_vacuum
LDEPART 200
ACCURACY 500 ALWAYS
END
RETURN
.END
.PROGRAM vacuumtest()
;CAUTION ROBOT WILL MOVE! WATCH OUT FOR OBJECTS IN RANGE
SPEED 100 ALWAYS
tellertje = 0
SPEED 10
JMOVE #gestrekt
TWAIT 5
SIGNAL o_zuiger
TWAIT 10
1 JMOVE #testpos1
TWAIT 2
JMOVE #testpos2
TWAIT 2
tellertje = tellertje+1
IF tellertje>=5 THEN
GOTO einde
ELSE
GOTO 1
END
einde:
SPEED 10
JMOVE #gestrekt
TWAIT 10
SIGNAL -o_zuiger
IGNORE 1013
.END
.PROGRAM viscalib()
SPEED 10 ALWAYS
ACCURACY 1 ALWAYS
JMOVE calib1
WHILE SIG(-s_gekalibreerd) DO
LMOVE calib1
TWAIT 2
LMOVE calib2
TWAIT 2
LMOVE calib4
TWAIT 2
LMOVE calib3
TWAIT 2
END
JMOVE #thuis
SPEED 100 ALWAYS
RETURN
.END -
.....'destruct test'.......sorry old habits again..............
- Not in the literal sense obviously, but when I make mods/create new I always test it out for holes/bugs....that's what I meant.
- If I can introduce issues conventionally from a 'day to day' operation, then I consider it potentially weak...
- In my experience, operators (not intentionally) highlight these during use, especially if there is an element of interaction on their part.
- The worse part of applying a change is being half way up the road and receiving a phone call.
- Returning and discovering an oversight......I call it 'belt and braces'.
- Purely dependent on just how complex the mod/change has been of course........Which SWAIT commands are you referring to - there are many?
- Never use SWAIT with signals within parenthesis (brackets), the command is 'evaluated' instead.
- The result is NOT the signal no. you are waiting for, so therefore it doesn't wait.
- I would check this......but definately remove the parentheses from all commands like:
- SWAIT (i_wt_aanwezig), SWAIT (i_palletinpos), SWAIT (-i_metenbezet) etc etc...
- I think this maybe where your problem is. -
Ah thanks bro!
I did the parentheses because the guys that worked on the robot before, used that same method! But thanks a lot!
How do the parentheses affect the structure controls like IF SIG (2002) THEN.. etc.?
Thanks! -
They are required in that context....'if it is THEN' Do something......if not, GOTO or ELSE or END.
- So very basic OR gate if required.SWAIT, this an actual condition command it is dedicated for exact SIGNALS status match and prevents forward planning until the signal condition matches the command.
- It also produces a 'pause' icon on the teach pendant - teach screen too.You can also use a WAIT command, but WAIT is not specific to signals, it can have multiple conditional checks such as signals, variables and timer values - but does not produce a 'pause' icon.
You could write it like:
WAIT (SIG(1001) AND SIG(1) AND NOT SIG(2001)); is exactly the same.Usually it is purely the programmers preference that you get variations of 'waiting', and so don't be surprised if you come across WAIT for signals instead of SWAIT.
- I believe SWAIT was introduced in the AS language later on as a command. -
Thanks! I'm gonna keep on using SWAIT!
