How can I increase enabled ref positions. I set for 20 ref position, but only first 10 will enable.
thanx
ref position
slamcity -
October 23, 2014 at 3:42 PM -
Pretty sure it is this variable:
$REFPOSMASK[1].$MAXREFPOSEN
you cannot access that variable on 8.3 for some reason, however you can still change $REFPOSMAXNO and then change the values inside each field of $REFPOS1[#]
interestingly enough this lets you change the output signal to somthing other than a RO or DO. the default setting for $REFPOS1[1].$DOUT_TYPE = 2 (Digital Out) this can be changed to anything you need. for example 35 sets it to a Flag. $REFPOS1[1].$DOUT_INDX = output number desired.
for a full ist of io types you can check out kliotyps.kl. this file should be included with any installation of Roboguide products including OLPC or WinOLPC.
Same on v8.1.
Even if you can't access it directly from the teach pendant system variables screen, you can still write to it using a TP program.
By default it is set to 10, meaning only 10 ref positions are allowed to be active at one time.
Here is a program to set it to 20:
i suspect it will get fixed in an auto update. 8.30/03 does not let me even run that program. i cant even view the variable in roboguide either. i didnt try in karel yet, but after it reboots it must update the mask itself as i can modify the ref pos from the menus.
Thanx, It worked perfect!!!