See this post for some helpful information about changing from X11 to PROFIsafe.
PostRE: Changing X11 saffety to ProfiSafe
to change interface from ProfiSafe to X11 you need to
1. power up
2. collect fresh project from robot (or make archive or image, that should collect them all)
3. power down cabinet
4. install SIB board (single thumb screw)
5. make sure it is powered correctly (see schematics, A1.PMB.X302 - A3.SIB.X250 using cable W188678)
6. make sure it is networked correctly (see schematics, A1.CCU.X48 to A3.SIB.X258 using cable W189363)
7. remove one of blank plates and install X11 interface.
8. connect X11…panic modeJune 29, 2022 at 3:56 PM
Hi DS186. I have checked the post before I creating the new post.
In fact, I have done many KRC4 Standard Cabinets before. And I can say, the Standard Ver. does NOT need to remove the power supply for SIB. And does not required X311 connector.
BUT I don't know how to do in the COMPACT Ver.
Any way, Thanks your very useful info.