Hi SkyeFire,
The robot comes with Profinet Profisafe device v3.2.
In work visual -> Profinet IO, I can only see 0 or 64 in 'no of safe IOs' column.
There is no safe operation installed!
I tried with X11 disconnected and Connected. In both cases, It doesn't affect the error messages, 'Safe device communication error' and 'Safety Stop'.
I tried with 0 safe IOs from robot side, deleted 64 safe IOs in Siemens GSD device, in order to establish only Profinet connection. I had a successful connection and normal 256 IOs are working fine.
It is only when i selected 64 safe IOs on Robot side and PLC side, i got this error back!
After disconnecting X11 connector, do I have to make any more hardware changes ?
The profinet safety ID in Robot is 7.
On PLC KRC4 GSD - f_source_add: 7, f_dest_add: 7, F_WD_Time: 250ms
PLC s7 1511 F-1 PN - low limit for f destination add: 1, high limit for f destination address: 99, central f source address: 7, default f_monitoring time: 250ms
Did I address them correctly ?
Do I have to map the 64 safety inputs somewhere in safety program?