you can purchase a dummy plug from Fanuc to do this.
Posts by Iprogram
-
-
Is the robot set up as an adapter in slot #1 under the Ethernet IP list?
-
Hello All,I want to use the PPABN (Pneumatic Pressure Abnormal) logic without having to run a cable from the base of the robot (pressure sensor) to the End Effector input.
Right now I have it wired into a regular digital input with a user alarm but want to monitor this input without constantly doing a Wait DI(108)=ON statement.
BG Logic can't call a user alarm either.
Any suggestions?
Background logic cannot set a user alarm buy you can use the BG logic to set an output based on the input or use a condition handler to set the alarm based on the input. OR a macro could do the alarm. many ways to do it.
-
-
Why are you trying to group the RO/RI to GO/GI. is it for robot to plc comunication? need more info
-
Not sure about that? What are you trying to do with the RI/RO to GI/GO?
-
Would need a backup for this issue. too many things could be going on. How is it getting a pick ready signal? is it in a teach pendant program?
-
I have a M-410iB R30iB controller and I would like to use the Panel Wizard to make a simple screen to jog a conveyor. I would like the button to be momentary and not a toggle but cant seem to find one. Do they have this option in the Free panel wizard software? I can get it to work using the toggle but only want the conveyor to move when the button is pushed.
Any idea's